SRT5KXLI with firmware v. 04.7 , but external packs on v. 04.1

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRT5KXLI with firmware v. 04.7 , but external packs on v. 04.1
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:54 AM . Last Modified: ‎2024-03-17 11:45 PM

0 Likes
17
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:54 AM . Last Modified: ‎2024-03-17 11:45 PM

SRT5KXLI with firmware v. 04.7 , but external packs on v. 04.1

Hello All,

I have a question, our company received new UPS APC SRT5KXLI with version of UPS 04.7 (checked from UPS NMC card web interface), but when I trying to find this firmware in official site of APC, the latest available version for this model is 04.1.

UPS is working fine, but I need my 2 external packs(they were been upgraded before to 04.1) recognized and identified by UPS.

What to do? Please your support.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

Hi Sultan

Can you reply to the last email you received from our Customer care email system so the troubleshooting can be done with a customer care agent.  The forum isn't the best way of resolving these problems or is it intended for this purpose.

Thanks

Matt

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 17
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:54 AM . Last Modified: ‎2024-03-17 11:45 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:54 AM . Last Modified: ‎2024-03-17 11:45 PM

Hi Sultan

Can you contact your local APC Customer Care team on +7 495 777 99 88, they will be able to send you the firmware file to update the Battery packs.

Thanks

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:54 AM . Last Modified: ‎2024-03-17 11:45 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:54 AM . Last Modified: ‎2024-03-17 11:45 PM

Hello Matt,

Can you please send this firmware to my e-mail? My local APC Customer Care team still not send me (2 weeks passed from my request).

I have sent an e-mail to you.

Big thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:54 AM . Last Modified: ‎2024-03-17 11:45 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:54 AM . Last Modified: ‎2024-03-17 11:45 PM

Hi

I have replied with an updated firmware for you.  The customer care team had emailed me, not knowing I was out of the office

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:54 AM . Last Modified: ‎2024-03-17 11:45 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:54 AM . Last Modified: ‎2024-03-17 11:45 PM

Thank you!

I'll try and inform you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:54 AM . Last Modified: ‎2024-03-17 11:45 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:54 AM . Last Modified: ‎2024-03-17 11:45 PM

Hello Matt,

I've tried upgrade via USB with Firmware Upgrade Wizard 4.1.1 but I every time get this error (attached).

Please your support and help.

Thank you.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:45 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:45 PM

Hi Sultan

If you have unpacked the firmware wizard to the default location, you should have a log file, FUW.log in C:\temp

Could you send that to me to look at 

Thanks

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:44 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:44 PM

Hello Matt,

I've sent log file to your e-mail.

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:44 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:44 PM

Thanks

the log file shows 'UPS is not in proper state to accept file, aborting the File Transfer'

  • Can you disconnect all power to the UPS (both AC utility power and Internal and External battery packs)
  • Reconnect it again.
  • Make sure the output is turned off 
  • Try again to use firmware wizard to update the UPS with 4.8 firmware file

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:44 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:44 PM

I've tried even via Serial, same error.

UPS should be turned on, but output off?

Ok, I'll try and inform you.

Thank you!

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:44 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:44 PM

On 10/10/2018 2:42 PM, Matt said:

Thanks

the log file shows 'UPS is not in proper state to accept file, aborting the File Transfer'

  • Can you disconnect all power to the UPS (both AC utility power and Internal and External battery packs)
  • Reconnect it again.
  • Make sure the output is turned off 
  • Try again to use firmware wizard to update the UPS with 4.8 firmware file

Matt

Hello Matt,

I think this problem due of APC battery not showing in Device Manager->Batteries.

Do you have some instructions what to do?

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:28 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:28 PM

It seems that FUW ruining my USB and battery connection for Windows. When I exit from FUW it's ok all in device manager. When I start FUW, all is gone. Please send me FUW 4.1 or FUW 4.0 Thank you.
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:28 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:28 PM

Hi sultan 

Unfortunately I do not have access to earlier versions of the firmware upgrade wizard.  If you have a Neetwork Management Card installed it is possible to update the firmware via that also.

Regards

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:28 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:28 PM

On 10/11/2018 5:48 PM, Matt said:

Hi sultan 

Unfortunately I do not have access to earlier versions of the firmware upgrade wizard.  If you have a Neetwork Management Card installed it is possible to update the firmware via that also.

Regards

Matt

Hello Matt,

Is it safe to upgrade via NMC ?

My UPS connected to the switch and has static IP.

If upgrade will fail, how to recover UPS?

Thank you.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:27 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:27 PM

Hi Sultan - 

It is safe to upgrade via the NMC, however the UPS output must be turned off for that method as well. You cannot upgrade the firmware on this UPS with the output on.

If you're still having issues with the firmware upgrade even when the output is turned off I would suggest contacting your local tech support team.

Thanks

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:27 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:55 AM . Last Modified: ‎2024-03-17 11:27 PM

On 10/12/2018 9:05 PM, Liam said:

Hi Sultan - 

It is safe to upgrade via the NMC, however the UPS output must be turned off for that method as well. You cannot upgrade the firmware on this UPS with the output on.

If you're still having issues with the firmware upgrade even when the output is turned off I would suggest contacting your local tech support team.

Thanks

Liam

Hello Liam,

Thank you, I've updated successfully via NMC.

But my main issue still not resolved - external battery packs not recognizing.

Please your advices.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

0 Likes
0
3636
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

One of external battery packs was recognized, Health OK, but Status Warning.

Pack status - General error.

NMC shows as 

1 Critical Alarm Present
  • Battery general error for battery pack 1.    Please your help!
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

0 Likes
0
3637
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

Hi Sultan

Can you reply to the last email you received from our Customer care email system so the troubleshooting can be done with a customer care agent.  The forum isn't the best way of resolving these problems or is it intended for this purpose.

Thanks

Matt

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore