Smart-UPS 3000 communications and runtime issue

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Smart-UPS 3000 communications and runtime issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

0 Likes
3
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

Smart-UPS 3000 communications and runtime issue

I have an old Smart-UPS that has served me well for years. Other than changing batteries it has been solid. I used to have it connected to a computer with Powerchute but it was awhile ago and I remember that it was a PITA to get it to connect and communicate. I haven't had it connected to Powerchute for a few years since reformatting the PC I use. Well, a couple months ago I started getting the flashing full LEDs indicating not enough run time for my load (which is only about 25% load according to the panel LEDs). I changed the batteries and they charged up. But, with a 25% load, I still get the full flashing LEDs. So I tried a manual calibration. I had approx 25% (I know 30% is recommended) load and let it power the load disconnected from mains and it shut down after about 10 min. If I recall, when I did this years ago, it would show low battery quickly for a long time when calibrating manually. Like it "thought" it was low (1 LED) but would run until it actually got too low and shut off, thus the calibration process. It didn't do that this time and checking the batteries after it shut off, they were still over 13v each.

Well I figured I would try using Powerchute for a calibration. This UPS has 3 serial ports, one built in and an expansion card with 2. I do not recall which I used previously. I have an APC USB conversion cable (AP9584) and a standard usb to serial adapter. I tried both of these on all ports (the built in one doesn't even wake the adapter) and can not get any communication via Powerchute. Using the APC adapter it shows up in device manager correctly under HID devices as an APC power connection (don't recall the exact term). I have tried older versions of Powerchute business and the most recent version. It never detects the UPS during the auto detect process or when selecting different options manually. In the latest version of Powerchute there are 4 different connection options and many "UPS Types". I tried many of them but assumed it should be the "SU" type. When I click the help option link for "How to determine the USP type" it goes to the support page and not a direct help topic.

Whew, lots of info, just wanted to make sure I gave all info needed.

So, during the manual calibration, should I have more of a load? Would that force the calibration to be correct? Or, can anyone provide some pointers on getting this thing to communicate with Powerchute?

Picture attached to show exact model

Thanks

Attachments
Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

0 Likes
0
938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

Do you have the serial number off the UPS? Were the batteries genuine APC? If so - Could I get the serial number off of those?

The ports on the expansion slot are simple signaling ports. They can tell you If the UPS is online, on battery, or at low battery. To actually get any useful information from the UPS you would need to use the port on the UPS itself with a 940-0024 or 940-1524 cable. We don't support USB adapters with these units, but if you were to try one it would have to be in conjunction with one of those two cables.

Since these are new batteries, I would attempt doing the manual calibration again with at least a 30% load (more is better). Wait until the UPS drops the load, then plug the unit back in and allow to charge to 100%. If that doesn't resolve the issue you can try contacting tech support and requesting a Calibration Key (Part #940-0260). They should be able to send it out free of charge. It's important to remember that this unit is quite old and may have other issues above and beyond what a calibration cab resolve.

Thanks

Liam

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

0 Likes
0
938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

Hi John - 

Can I get the model and serial number off of the UPS? Do you know how old the batteries are in the UPS? Given the behavior, it is likely bad batteries.

To communicate you would want to use the serial port on the UPS chassis itself, not either of the ones on the expansion card. You would need the proper cable, which would be labeled 940-0024 or 940-1524. It should be able to auto detect the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

0 Likes
0
940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

The batteries were just replaced and as described above, after the unsuccessful manual calibration they were all still over 13 volts. When using the serial port on the chassis, nothing shows up in device manager. The only way I can get a port to show up in device manager is to use one of the expansion connections with the APC USB conversion cable (AP9584). The actual model is DL3000rm3u.

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

0 Likes
0
939
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 08:56 AM . Last Modified: ‎2024-03-17 11:27 PM

Do you have the serial number off the UPS? Were the batteries genuine APC? If so - Could I get the serial number off of those?

The ports on the expansion slot are simple signaling ports. They can tell you If the UPS is online, on battery, or at low battery. To actually get any useful information from the UPS you would need to use the port on the UPS itself with a 940-0024 or 940-1524 cable. We don't support USB adapters with these units, but if you were to try one it would have to be in conjunction with one of those two cables.

Since these are new batteries, I would attempt doing the manual calibration again with at least a 30% load (more is better). Wait until the UPS drops the load, then plug the unit back in and allow to charge to 100%. If that doesn't resolve the issue you can try contacting tech support and requesting a Calibration Key (Part #940-0260). They should be able to send it out free of charge. It's important to remember that this unit is quite old and may have other issues above and beyond what a calibration cab resolve.

Thanks

Liam

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore