SRT5KXLI with firmware v. 04.7 , but external packs on v. 04.1
Hello All,
I have a question, our company received new UPS APC SRT5KXLI with version of UPS 04.7 (checked from UPS NMC card web interface), but when I trying to find this firmware in official site of APC, the latest available version for this model is 04.1.
UPS is working fine, but I need my 2 external packs(they were been upgraded before to 04.1) recognized and identified by UPS.
What to do? Please your support.
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:56 AM . Last Modified: 2024-03-17 11:27 PM
Hi Sultan
Can you reply to the last email you received from our Customer care email system so the troubleshooting can be done with a customer care agent. The forum isn't the best way of resolving these problems or is it intended for this purpose.
Thanks
Matt
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:54 AM . Last Modified: 2024-03-17 11:45 PM
Hi Sultan
Can you contact your local APC Customer Care team on +7 495 777 99 88, they will be able to send you the firmware file to update the Battery packs.
Thanks
Matt
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 08:54 AM . Last Modified: 2024-03-17 11:45 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:54 AM . Last Modified: 2024-03-17 11:45 PM
Hello Matt,
Can you please send this firmware to my e-mail? My local APC Customer Care team still not send me (2 weeks passed from my request).
I have sent an e-mail to you.
Big thanks.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:54 AM . Last Modified: 2024-03-17 11:45 PM
Hi
I have replied with an updated firmware for you. The customer care team had emailed me, not knowing I was out of the office
Thanks
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 08:54 AM . Last Modified: 2024-03-17 11:45 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:54 AM . Last Modified: 2024-03-17 11:45 PM
Thank you!
I'll try and inform you.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 08:54 AM . Last Modified: 2024-03-17 11:45 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:54 AM . Last Modified: 2024-03-17 11:45 PM
Hello Matt,
I've tried upgrade via USB with Firmware Upgrade Wizard 4.1.1 but I every time get this error (attached).
Please your support and help.
Thank you.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:45 PM
Hi Sultan
If you have unpacked the firmware wizard to the default location, you should have a log file, FUW.log in C:\temp
Could you send that to me to look at
Thanks
Matt
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:44 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:44 PM
Hello Matt,
I've sent log file to your e-mail.
Thank you.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:44 PM
Thanks
the log file shows 'UPS is not in proper state to accept file, aborting the File Transfer'
- Can you disconnect all power to the UPS (both AC utility power and Internal and External battery packs)
- Reconnect it again.
- Make sure the output is turned off
- Try again to use firmware wizard to update the UPS with 4.8 firmware file
Matt
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:44 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:44 PM
I've tried even via Serial, same error.
UPS should be turned on, but output off?
Ok, I'll try and inform you.
Thank you!
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:44 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:44 PM
On 10/10/2018 2:42 PM, Matt said:Thanks
the log file shows 'UPS is not in proper state to accept file, aborting the File Transfer'
- Can you disconnect all power to the UPS (both AC utility power and Internal and External battery packs)
- Reconnect it again.
- Make sure the output is turned off
- Try again to use firmware wizard to update the UPS with 4.8 firmware file
Matt
Hello Matt,
I think this problem due of APC battery not showing in Device Manager->Batteries.
Do you have some instructions what to do?
Thank you.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:28 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:28 PM
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:28 PM
Hi sultan
Unfortunately I do not have access to earlier versions of the firmware upgrade wizard. If you have a Neetwork Management Card installed it is possible to update the firmware via that also.
Regards
Matt
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:28 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:28 PM
On 10/11/2018 5:48 PM, Matt said:Hi sultan
Unfortunately I do not have access to earlier versions of the firmware upgrade wizard. If you have a Neetwork Management Card installed it is possible to update the firmware via that also.
Regards
Matt
Hello Matt,
Is it safe to upgrade via NMC ?
My UPS connected to the switch and has static IP.
If upgrade will fail, how to recover UPS?
Thank you.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:27 PM
Hi Sultan -
It is safe to upgrade via the NMC, however the UPS output must be turned off for that method as well. You cannot upgrade the firmware on this UPS with the output on.
If you're still having issues with the firmware upgrade even when the output is turned off I would suggest contacting your local tech support team.
Thanks
Liam
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:27 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:55 AM . Last Modified: 2024-03-17 11:27 PM
On 10/12/2018 9:05 PM, Liam said:Hi Sultan -
It is safe to upgrade via the NMC, however the UPS output must be turned off for that method as well. You cannot upgrade the firmware on this UPS with the output on.
If you're still having issues with the firmware upgrade even when the output is turned off I would suggest contacting your local tech support team.
Thanks
Liam
Hello Liam,
Thank you, I've updated successfully via NMC.
But my main issue still not resolved - external battery packs not recognizing.
Please your advices.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-28 08:56 AM . Last Modified: 2024-03-17 11:27 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:56 AM . Last Modified: 2024-03-17 11:27 PM
One of external battery packs was recognized, Health OK, but Status Warning.
Pack status - General error.
NMC shows as
- Battery general error for battery pack 1. Please your help!
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 08:56 AM . Last Modified: 2024-03-17 11:27 PM
Hi Sultan
Can you reply to the last email you received from our Customer care email system so the troubleshooting can be done with a customer care agent. The forum isn't the best way of resolving these problems or is it intended for this purpose.
Thanks
Matt