Just encountered a very strange problem while doing a first ever calibration on one SMX1500 and two SMX750's simultaneously... started the calibration remotely via the web interface (all have AP9631''s at bootmon 1.0.2 / AOS/SUMX at rev 5.1.7 ) and not one of them is reporting the calibration ending - and this is well after the batteries drained to 25% and recharged completely per the usual process. When i log into the cards, the main screen shows "Battery Calibration in Progress" and under the UPS/Diagnostics tab it still says "Calibration: In progress".
...another firmware bug to fix, possibly ?
Now I am wondering what to do; try to end the calibration manually ? reboot the card ?
I'm a bit worried I might crash the ups or something if I attempt either...
Does anyone from APC have any info on this ?
Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:38 AM . Last Modified: 2024-03-13 01:38 AM
ok, let's start with a firmware upgrade on the UPS itself. when you do this, the UPS output will need to be turned off.
i will contact you offline to help you on how to accomplish this.
as far as this issue - i would start by rebooting the network management card to see if it clears but then someone else told me it may require turning the UPS on/off when we might as well just upgrade the firmware at that point anyway.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:38 AM . Last Modified: 2024-03-13 01:38 AM
can you tell me what firmware is on the UPS itself under UPS->About.
I think that I have seen this before and it is an issue with the UPS versus the NMC. I'll double check it when I have your UPS firmware info so I can verify. rebooting the NMC management interface would not affect the UPS output.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:38 AM . Last Modified: 2024-03-13 01:38 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:38 AM . Last Modified: 2024-03-13 01:38 AM
The SMX750's are all as follows:
Firmware Revision: UPS 03.6 / COM 03.6 / UBL 05.0 / CBL 02.1 (ID11)
Manufacture Date: 10/01/2010
The SMX1500 is as follows:
Firmware Revision: UPS 03.7 / COM 03.6 / UBL 05.0 / CBL 02.1 (ID11)
Manufacture Date: 01/28/2011
For now should I tell the ups to "cancel the calibration" or just reboot the card ?
Any info appreciated, Thanks!
Dave
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:38 AM . Last Modified: 2024-03-13 01:38 AM
ok, let's start with a firmware upgrade on the UPS itself. when you do this, the UPS output will need to be turned off.
i will contact you offline to help you on how to accomplish this.
as far as this issue - i would start by rebooting the network management card to see if it clears but then someone else told me it may require turning the UPS on/off when we might as well just upgrade the firmware at that point anyway.