SMX750/1500 Calibration not ending properly (AP9631 with 5.1.7 firmware)
Just encountered a very strange problem while doing a first ever calibration on one SMX1500 and two SMX750's simultaneously... started the calibration remotely via the web interface (all have AP9631''s at bootmon 1.0.2 / AOS/SUMX at rev 5.1.7 ) and not one of them is reporting the calibration ending - and this is well after the batteries drained to 25% and recharged completely per the usual process. When i log into the cards, the main screen shows "Battery Calibration in Progress" and under the UPS/Diagnostics tab it still says "Calibration: In progress".
...another firmware bug to fix, possibly ?
Now I am wondering what to do; try to end the calibration manually ? reboot the card ?
I'm a bit worried I might crash the ups or something if I attempt either...
Does anyone from APC have any info on this ?
Thanks!
- Labels:
-
Smart-UPS & Symmetra LX | RM
Authentication Failed.
- Authentication Ticket Mismatched, failed authentication.
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:38 AM . Last Modified: 2024-03-13 01:38 AM
ok, let's start with a firmware upgrade on the UPS itself. when you do this, the UPS output will need to be turned off.
i will contact you offline to help you on how to accomplish this.
as far as this issue - i would start by rebooting the network management card to see if it clears but then someone else told me it may require turning the UPS on/off when we might as well just upgrade the firmware at that point anyway.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:38 AM . Last Modified: 2024-03-13 01:38 AM
can you tell me what firmware is on the UPS itself under UPS->About.
I think that I have seen this before and it is an issue with the UPS versus the NMC. I'll double check it when I have your UPS firmware info so I can verify. rebooting the NMC management interface would not affect the UPS output.
Link copied. Please paste this link to share this article on your social media post.

Posted: 2021-06-29 04:38 AM . Last Modified: 2024-03-13 01:38 AM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:38 AM . Last Modified: 2024-03-13 01:38 AM
The SMX750's are all as follows:
Firmware Revision: UPS 03.6 / COM 03.6 / UBL 05.0 / CBL 02.1 (ID11)
Manufacture Date: 10/01/2010
The SMX1500 is as follows:
Firmware Revision: UPS 03.7 / COM 03.6 / UBL 05.0 / CBL 02.1 (ID11)
Manufacture Date: 01/28/2011
For now should I tell the ups to "cancel the calibration" or just reboot the card ?
Any info appreciated, Thanks!
Dave
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:38 AM . Last Modified: 2024-03-13 01:38 AM
ok, let's start with a firmware upgrade on the UPS itself. when you do this, the UPS output will need to be turned off.
i will contact you offline to help you on how to accomplish this.
as far as this issue - i would start by rebooting the network management card to see if it clears but then someone else told me it may require turning the UPS on/off when we might as well just upgrade the firmware at that point anyway.