Transfer inhibit - comparatively what is it in the APC world?

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Transfer inhibit - comparatively what is it in the APC world?
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
110
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 04:38 AM . Last Modified: ‎2024-03-13 01:38 AM

0 Likes
2
2311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:38 AM . Last Modified: ‎2024-03-13 01:38 AM

Transfer inhibit - comparatively what is it in the APC world?

This might not be the right place for this question - just hoping to find someone who might know;
I have background and years of experience with Symmetra LX - now in my current job I have a couple of comparative UPS (20Kva single tower) in a different brand, now and again, once per week perhaps, i get an alarm for a few seconds or a minute, saying "Transfer Inhibit" - which I have never seen before and I am not sure what it is, if there is a comparative alarm in the APC world I could compare to? This brand doesnt have a whole lot of useful documentation on it that I can find..
to me it sounds like the UPS is saying "Hey, your facility power is now so bad, I will not go to bypass if I fail, it is safer to drop the load" - but I am not certain that is what it says? - and how would I go about doing anything about it, never seen it on my Symmetra's, and they didnt exactly have "nice" utility feeds either...

here's the output in my alert email:
Events listed in chronological order.
Event: Active:Transfer Inhibit
Event: Active:Device Active Alarm
Event: Cleared:Device Active Alarm
Event: Cleared:Transfer Inhibit
Active Events: None

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • symmetra
  • ups
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:38 AM . Last Modified: ‎2024-03-13 01:38 AM

0 Likes
0
2309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:38 AM . Last Modified: ‎2024-03-13 01:38 AM

i'd also guess what you thought as well. i know we have this type of thing in our automatic transfer switches as well called "switch inhibit" where you can tell the ATS to not switch in certain situations and drop the load versus subjecting the load to a potentially bad input or shorted source.

i am guessing this relates to bypass being familiar with the LX myself.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 04:38 AM . Last Modified: ‎2024-03-13 01:38 AM

0 Likes
0
2309
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:38 AM . Last Modified: ‎2024-03-13 01:38 AM

>
"Hey, your facility power is now so bad, I will not go to bypass if I fail, it is safer to drop the load" - but I am not certain that is what it says? - and how would I go about doing anything about it, never seen it on my Symmetra's, and they didnt exactly have "nice" utility feeds either...
>

If your facility feed exceeds the bypass limits in voltage or frequency, a Symmetra will complain about "Bypass out of range." The acceptable bypass range is configurable on the NMC under UPS->Power. Should also be somewhere on the PowerView display.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 04:38 AM . Last Modified: ‎2024-03-13 01:38 AM

0 Likes
0
2310
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 04:38 AM . Last Modified: ‎2024-03-13 01:38 AM

i'd also guess what you thought as well. i know we have this type of thing in our automatic transfer switches as well called "switch inhibit" where you can tell the ATS to not switch in certain situations and drop the load versus subjecting the load to a potentially bad input or shorted source.

i am guessing this relates to bypass being familiar with the LX myself.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of