Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

SMT750IC vs SMV750CAI

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT750IC vs SMV750CAI
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
140
View All

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
sib2024
Crewman sib2024
Crewman

Posted: ‎2025-01-20 09:52 AM

0 Likes
1
423
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-01-20 09:52 AM

SMT750IC vs SMV750CAI

Hello 

Regarding those two items 

SMT750IC vs SMV750CAI

I don’t need notification for events but I cannot decide between those two models .

The only notable difference that I found is that the SMV has lower surge protection 190J , and the SMT has higher surge protection 540J, and connectivity differences between them.

How much matters the surge protection value ?

I want to protect a sound system and a smart tv , I understand that , for avoiding disturbing noise in audio systems it’s necessary to have a sine wave electric power.

Also in another place , I want to protect an ornamental fireplace that requires sine wave electric power .

Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-17 05:19 AM

0 Likes
0
348
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-17 05:19 AM

Hello,

 

Both units are working in line interactive topology and provide pure sine wave but on only battery mode as in this topology the inverter is in standby, in normal mode the UPS worked a AVR that regulates input voltage and provide boost/trim voltage compensation to the output, so it delivers variable voltage at this mode but it is regulated ,only the précised voltage applied to the load during inverter operation on battery mode

 

if the load is not sensitive so these units are ideal ,we recommends to buy SMT750IC as it had smart connect feature and you can insert AP9640 as an optional smart slot to get the benefits of our NMC 3 platform

 

SMV750CAI card APV9602 is discontinued and it recommended to consider  SMT model instead as shown below

 

https://www.se.com/uk/en/product/APVS9602/easy-ups-1ph-smvs-network-management-card/

 

Regards,

 

Karim

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Reply 1
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-17 05:19 AM

0 Likes
0
349
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-17 05:19 AM

Hello,

 

Both units are working in line interactive topology and provide pure sine wave but on only battery mode as in this topology the inverter is in standby, in normal mode the UPS worked a AVR that regulates input voltage and provide boost/trim voltage compensation to the output, so it delivers variable voltage at this mode but it is regulated ,only the précised voltage applied to the load during inverter operation on battery mode

 

if the load is not sensitive so these units are ideal ,we recommends to buy SMT750IC as it had smart connect feature and you can insert AP9640 as an optional smart slot to get the benefits of our NMC 3 platform

 

SMV750CAI card APV9602 is discontinued and it recommended to consider  SMT model instead as shown below

 

https://www.se.com/uk/en/product/APVS9602/easy-ups-1ph-smvs-network-management-card/

 

Regards,

 

Karim

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore