PCNS for Azure Stack HCI Cluster

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS for Azure Stack HCI Cluster
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BBM
BBM
Cadet

Posted: ‎2025-02-04 02:16 AM . Last Modified: ‎2025-02-04 02:16 AM

0 Likes
4
1128
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-04 02:16 AM . Last Modified: ‎2025-02-04 02:16 AM

PCNS for Azure Stack HCI Cluster

Hi everyone,

we have an environment with 2 somewhat larger UPSs which protect various servers (incl. 1 cluster with 3 nodes, Azure Stack HCI). In the event of a power failure, we would like to shut down our VMs in a certain order. Unfortunately, I have not yet been able to test the PCNS software properly and have not found any correct installations or configurations for Hyper-V or Azure Stack HCI.
Does anyone know anything about this or is PCNS even the right choice for the software?
We do not use SCVMM in our company.
Regards

 

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-11 03:32 AM

0 Likes
1
1089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-11 03:32 AM

Hello,

 

You can find all the instruction for installation and configuration in the below manual step by step for Hyper-V & SCVMM

 

https://download.schneider-electric.com/files?p_Doc_Ref=SPD_PMAR-9E5LP4_EN&p_enDocType=User+guide&p_...

 

PCNS is compatible with Azur stack HCI as per OS compatibility  chart below 

 

https://download.schneider-electric.com/files?p_Doc_Ref=SPD_SJHN-7AYQNP_EN&p_enDocType=User+guide&p_...

 

Configuring Virtual Machines to shut down when a Hyper-V host is commanded to shut down is explained in the below FAQ:

https://www.apc.com/nl/en/faqs/FA159689/

 

but PCNS license is required to be purchased to support the virtualization  feature as per the below :

 

https://download.schneider-electric.com/files?p_Doc_Ref=SPD_PCNS_FAQ_EN&p_enDocType=Instruction+shee...

 

But you can use  The unlicensed PowerChute Network Shutdown  to protect a Hyper-V Host with the Hyper-V Manager as per the attachment 

 

Regards,

 

Karim

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-11 03:32 AM

0 Likes
1
1090
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-11 03:32 AM

Hello,

 

You can find all the instruction for installation and configuration in the below manual step by step for Hyper-V & SCVMM

 

https://download.schneider-electric.com/files?p_Doc_Ref=SPD_PMAR-9E5LP4_EN&p_enDocType=User+guide&p_...

 

PCNS is compatible with Azur stack HCI as per OS compatibility  chart below 

 

https://download.schneider-electric.com/files?p_Doc_Ref=SPD_SJHN-7AYQNP_EN&p_enDocType=User+guide&p_...

 

Configuring Virtual Machines to shut down when a Hyper-V host is commanded to shut down is explained in the below FAQ:

https://www.apc.com/nl/en/faqs/FA159689/

 

but PCNS license is required to be purchased to support the virtualization  feature as per the below :

 

https://download.schneider-electric.com/files?p_Doc_Ref=SPD_PCNS_FAQ_EN&p_enDocType=Instruction+shee...

 

But you can use  The unlicensed PowerChute Network Shutdown  to protect a Hyper-V Host with the Hyper-V Manager as per the attachment 

 

Regards,

 

Karim

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

BBM
BBM
Cadet

Posted: ‎2025-02-11 04:28 AM

In response to KarimEissa
0 Likes
0
1074
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-11 04:28 AM

Hi Karim,
Unfortunately, I am already familiar with these articles and manuals. But I haven't really been able to find anything on how to install the software for the Azurestack HCI cluster and define the prioritization of the virtual machines there?
Are there any documents, training courses or services that could help me with PCNS and Azurestack HCI?

 

Regards
Björn Meier

Reply

Link copied. Please paste this link to share this article on your social media post.

KarimEissa
Commander KarimEissa Commander
Commander

Posted: ‎2025-02-16 04:32 AM

0 Likes
1
1017
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-16 04:32 AM

Hello,

 

You can enroll in PCNS e-learning course from the below link

 

https://download.schneider-electric.com/files?p_Doc_Ref=SPD-PCNS_ELEARN_EN&p_enDocType=EDMS

 

all the available documents are in this link

 

https://www.se.com/uk/en/product-range/61933-powerchute-network-shutdown/#documents

 

Regards,

 

Karim

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

BBM
BBM
Cadet

Posted: ‎2025-02-17 03:01 AM

In response to KarimEissa
0 Likes
0
1001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-02-17 03:01 AM

Hi Karim,

i do the e-learnings too. But there are zero information how to handle PNCS with Azurestack HCI.
In the documents you cannot find anything about the PowerChute Software with Azurestack HCI and how to handle it.
Maybe I am blind but there is no installation guide for PNCS for Azurestack HCI. There is only the chart that said that PCNS is working with Azurestack HCI but not how.

Regards
Björn Meier

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore