SMT1500I ID=17 MODBUS

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT1500I ID=17 MODBUS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:43 AM . Last Modified: ‎2024-03-15 04:52 AM

0 Likes
5
1539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:43 AM . Last Modified: ‎2024-03-15 04:52 AM

SMT1500I ID=17 MODBUS

I have an SMT1500I ID=17 with the latest supported firmware 7.1

This firmware does not support MODBUS.

Since I use only Linux based servers I need MODBUS so that I can control the UPS with apcupsd/apcaccess

When is APC going to release a firmware for this model that supports MODBUS?

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 11:43 AM . Last Modified: ‎2024-03-15 04:52 AM

0 Likes
0
1538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:43 AM . Last Modified: ‎2024-03-15 04:52 AM

Thank you Bill,

I think that APC should make an effort to make this UPS compatible with apcupsd whether it be via MODBUS or a firmware upgrade that supports all the parameters in the old protocol.

I have much older SMART-UPS 1000 (one with the legacy SMART serial cable and one with USB) that work perfectly with apcupsd. I do not see why APC cannot make this one work like the older models too.

I am now waiting for the delivery of an AP9630, which I hope will resolve some of my problems allowing to control the UPS through the web interface.

 

Nevertheless it is unacceptable that APC refuses to make any more efforts in fixing this problem that they have created in the first place.

 

 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:43 AM . Last Modified: ‎2024-03-15 04:52 AM

0 Likes
0
1538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:43 AM . Last Modified: ‎2024-03-15 04:52 AM

Hi,

That version CPU will not support Modbus. However, you can use APCUPSD via USB. The difference is with USB com you will not get all of the info available via Modbus, but the computer will still be protected in the event of a power failure. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:43 AM . Last Modified: ‎2024-03-15 04:52 AM

0 Likes
0
1538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:43 AM . Last Modified: ‎2024-03-15 04:52 AM

Thank you, I already knew.

I am hereby asking APC to support MODBUS on SMT1500I ID=17 too.

APC created the problem by adopting a proprietary protocol not supported by 'apcupsd' and APC must fix the problem now by releasing a firmware that either support MODBUS or full control via Linux apcupsd on these models.

Failure to do that is unacceptable.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:43 AM . Last Modified: ‎2024-03-15 04:52 AM

0 Likes
0
1538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:43 AM . Last Modified: ‎2024-03-15 04:52 AM

Do APC staff ever look at customers' messages? I am using this forum because I tried before to contact them via the website contact form and it returns an error.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 11:43 AM . Last Modified: ‎2024-03-15 04:52 AM

0 Likes
0
1538
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:43 AM . Last Modified: ‎2024-03-15 04:52 AM

Mauro,

I am a Schneider Electric employee and I understand your need. However, as stated in my initial post that UPS hardware is not capable of the upgrade you are requesting.

As mentioned earlier you can use USB com to the shutdown of the OS with the firmware currently installed on the UPS. Other options are to upgrade the SMT1500i to an SMT1500Ci that will ship with Modbus accessibility pre-installed. Or install the AP9620 legacy communications card in the Smart slot and connect APCUPSD via USB or serial to the card. The AP9620 card translates the UPS Microlink protocol to UPSlink protocol and APCUPSD was written initially for UPSlink.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 11:43 AM . Last Modified: ‎2024-03-15 04:52 AM

0 Likes
0
1539
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 11:43 AM . Last Modified: ‎2024-03-15 04:52 AM

Thank you Bill,

I think that APC should make an effort to make this UPS compatible with apcupsd whether it be via MODBUS or a firmware upgrade that supports all the parameters in the old protocol.

I have much older SMART-UPS 1000 (one with the legacy SMART serial cable and one with USB) that work perfectly with apcupsd. I do not see why APC cannot make this one work like the older models too.

I am now waiting for the delivery of an AP9630, which I hope will resolve some of my problems allowing to control the UPS through the web interface.

 

Nevertheless it is unacceptable that APC refuses to make any more efforts in fixing this problem that they have created in the first place.

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore