Hello, i have one apc smart-ups xl modular 1500va
I changed the batteries as I received many messages that suggested that the error was due to the batteries, but unfortunately I immediately checked that the error persists and I receive the messages that you can see attached. what can it be due to?
during these messages all the LEDs on the ups blinknCDggWdwxcnLW6lahxo%2Bmg%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
Thank youqsmS1oC64%2F8HEQ%2FA1ljpAw%3D%3D&Rest-Api-Key=d3Bhc3F1aWw6NjM3MzU2MWEtNzYzMC00OTc5LTkyMTAtOTJjYTU0NGEwZWFl.png
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:43 AM . Last Modified: 2024-03-15 04:52 AM
The error messages are not related to the batteries as such, internal hardware fault is more than likely an issue with the charger or inverter, overload means that there is too much draw on the UPS output and high temperature is self explanatory.
Can you confirm that you used APC batteries or did you by third party replacements, this kind of thing can happen if the batteries aren't exactly "to spec".
Also try disconnecting the load from the UPS, then turn it off completely, disconnect the battery and the mains power. Now hold the power button for 5 seconds, leave the unit to cool and then connect the battery, mains power but not the load.
Check to see if the errors still appear.
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 11:43 AM . Last Modified: 2024-03-15 04:52 AM
The error messages are not related to the batteries as such, internal hardware fault is more than likely an issue with the charger or inverter, overload means that there is too much draw on the UPS output and high temperature is self explanatory.
Can you confirm that you used APC batteries or did you by third party replacements, this kind of thing can happen if the batteries aren't exactly "to spec".
Also try disconnecting the load from the UPS, then turn it off completely, disconnect the battery and the mains power. Now hold the power button for 5 seconds, leave the unit to cool and then connect the battery, mains power but not the load.
Check to see if the errors still appear.
-Gavan
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.