SMT1500I Battery warning

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SMT1500I Battery warning
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

0 Likes
7
2001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

SMT1500I Battery warning

I have a SMT1500I which has just had its battery replaced. The unit is continually giving the warning 'no battery connected'. Is there any diagnostics I can perform or hard resets available?

Unit info is as follows

Smart UPS: SMT1500I
AS1148112065
UPS Firmware 1: UPS 05.0
UPS Firmware 2: COM 02.1
UPS Firmware 3: UBL 05.0
UPS Firmware 4: CBL 5.21

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

0 Likes
0
2000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

So, I bought a second battery. Serial shows as 14 and ... works first time! Thank you for the help!

See Answer In Context

  • Tags:
  • .
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

0 Likes
0
2000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

Was this an APC-branded RBC battery or one of the 3rd-party "reuse your existing cables and connectors" ones? If the latter, since there is more than one actual battery, is it possible you connected the wiring improperly? The APC one would have a single connector which only plugs in one way.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

0 Likes
0
2000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

No was an original branded APC battery. Slightly worried I may be just throwing good money at it by buying another... I'm going to try and upgrade the firmware as the next port of call..

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

0 Likes
0
2000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

Did it also give the "No battery connected" error before you replaced the battery, or a different message?

Since you have an APC battery, it should have an APC serial number sticker with the RBCxx part number and a serial number of the form "xxyynnnnnnnn" where yy represents the year of manufacture. Can you confirm it is 15? Or possibly 14, if it has been sitting in a warehouse somewhere.

Do you have a multimeter or DC voltmeter? Can you disconnect the battery and measure the voltage on the battery connector? I believe this pack has 2 12V batteries, so you should see about 24 Volts DC at the connector.

Your UPS is from 2011 according to its serial number, so it almost definitely needed a new battery pack. My "rule of thumb" as an end user of the Smart-UPS is that the first battery replacement usually works well, but by the time that battery needs to be replaced, it is time to look for a new UPS as the second replacement won't last as long as expected. This is because I've found that the charging voltage of the UPS drifts out of spec (almost always to the high side) over time and overcharges the batteries.

If you need to replace the UPS, consider the APC Trade-UPS program where they give you a discount on a new unit in exchange for your old one. But compare the cost of that with the best discount you can get on a new one without trade-in to make sure you are getting the best deal.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

0 Likes
0
2000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

Terry,

Thank you for your response. The battery part number indicates 13.... It is giving a steady 24v.

Yes the unit was giving the "No battery connected" before replacement.

Guessing it's time for a new unit....

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

0 Likes
0
2000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

If the RBC serial number has 13 in the year field, it is at least 17 months old. I'd suggest that you shop elsewhere for your replacment UPS - aside from the problem with getting one with old batteries, I think the warranty starts at time of manufacture unless you have a receipt from an authorized reseller, in which case the warranty starts then as long as you provide that to APC when making a warranty claim.

If the place where you purchased the battery is (or says it is) an authorized APC reseller, you may want to PM Angela (since you may not want to name them here in the forum) so that she can have APC contact them and discuss inventory practices and stock rotation.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

0 Likes
0
2000
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

I would also make sure you've let the new battery charge up for at least a day. A weak, discharged battery can display this behavior and not be "seen" by the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

0 Likes
0
2001
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-07 10:45 PM . Last Modified: ‎2024-03-01 12:27 AM

So, I bought a second battery. Serial shows as 14 and ... works first time! Thank you for the help!

  • Tags:
  • .
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore