Resurrecting a SRT6KXLI with Error P.05

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Resurrecting a SRT6KXLI with Error P.05
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Anonymous user
Not applicable

Posted: ‎2021-10-14 01:04 AM . Last Modified: ‎2022-10-19 01:22 AM

0 Likes
4
9393
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-14 01:04 AM . Last Modified: ‎2022-10-19 01:22 AM

Resurrecting a SRT6KXLI with Error P.05

Hi everyone, thanks in advance for all your help and ideas.

 

I am resurrecting a SRT6KXLI with dual APCRBC140 battery packs that was retired because of a constant Power Sys Error 00020 fault that has now been resolved by upgrading to the latest firmware, UPS 05.1 ID1013, per this post 

 

https://community.se.com/t5/Datacenter-Forum/SRT8KXLI-Power-Sys-Error-00020/td-p/287698

 

I am now getting the following errors:

P.05 contact customer support

Connect battery, backup not available

and Internal comm fault 154 in the logs 

 

I suspect that the battery packs are now beyond reviving and that the UPS is telling me to get new ones.  Before I go and throw a lot of cash at buying 2 new battery packs, can anyone share some insight into the P.05 and Fault 154 please?

 

Thank you

Labels
  • Labels:
  • Datacenter UPS
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
APC_Matt
Lieutenant JG APC_Matt Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-14 05:25 AM

0 Likes
2
9386
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-14 05:25 AM

Hi

 

Error 154 is a Lost comms event with the output on, and P.05 is a backfeed relay weld.

 

The only thing you can try to remedy these two issues is to 'braindead' the UPS,  removing the AC power and disconnecting the batteries to completely power the ups down and then reconnect. If that doesn't work the ups would need replacing

 

Regards

 

Matt

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-10-14 05:43 AM

In response to APC_Matt
0 Likes
1
9384
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-14 05:43 AM

Thannks Matt.  What constitutes a lost comms event please?  Could it be between PowerChute and my PC?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

APC_Matt
Lieutenant JG APC_Matt Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-14 06:17 AM

In response to Anonymous user
0 Likes
0
9379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-14 06:17 AM

Hi

In this case it's referencing a loss of communication on the internal communication buss rather than between the UPS and powerchute.

 

Matt

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-10-14 09:03 AM

0 Likes
0
9370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-10-14 09:03 AM

Keeping this thread going in case anyone has had practical experience of how this relay issue was potentially resolved without an expensive APC repair please.  This is the second (of two) APC UPSes that has failed within 18 months of normal operating conditions, doesnt really inspire confidence in the brand, this unit being the warranty replacement for the first one that failed and is therefore out of  the original unit's 3 year warranty.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore