SRT8KXLI - Power Sys Error 00020

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • SRT8KXLI - Power Sys Error 00020
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

0 Likes
10
8091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

SRT8KXLI - Power Sys Error 00020

Dear Forum,

for protecting IT equipment i use

  • one NEW SRT8KXLI
  • several Smart-UPS 2200 and 1500
  • diesel generator

In case of power blackout the following happens

  • power from UPS battery
  • generator produces power (automatic)
  • switch from main power to generator power (automatic)
  • UPS no longer on battery

In case the blackout is fixed

  • UPS on battery
  • switch from generator power to main power (automatic)
  • UPS no longer on battery

Problem-description:

After an major blackout our new SRT8KXLI reacts with an 00020 Error and turned the output power off 

This error occurs after the blackout wos fixed which means -> after the automatic switching from generator power back to main power 

No problems with the 2200 and 1500 UPS

APC replaced the UPS

For testing the new SRT8KXLI we simulated an blackout (use of generator), with exactly the same result -> Power Sys Error 00020 and backfeed relay fault exists, and again no issues with UPS 2200, 1500

Here is the LOG:

  • interrupt main Power
    • 10/28/2015 03:00:29 Device UPS: On battery power in response to rapid change of input. 0x0109
    • 10/28/2015 03:00:29 Device UPS: Bypass not in range ; low voltage. 0x020F
    • 10/28/2015 03:00:29 Device UPS: Main input bad. 0x01B0
  • switch to generator power
    • 10/28/2015 03:00:50 Device UPS: No longer on battery power. 0x010A
    • 10/28/2015 03:00:50 Device UPS: Main input bad cleared. 0x01B1
    • 10/28/2015 03:00:49 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
  • 1h on generator power
    • 10/28/2015 03:48:45 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
    • 10/28/2015 03:48:45 Device UPS: Bypass not in range ; distorted waveform. 0x020F
    • 10/28/2015 03:21:40 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
    • 10/28/2015 03:21:40 Device UPS: Bypass not in range ; low voltage. 0x020F
    • 10/28/2015 03:01:36 Device UPS: An input voltage or frequency problem no longer prevents switching to bypass mode. 0x0210
    • 10/28/2015 03:01:35 Device UPS: Bypass not in range ; distorted waveform. 0x020F
  • interrupt generator power
    • 10/28/2015 04:00:49 Device UPS: Bypass not in range ; low voltage. 0x020F
    • 10/28/2015 04:00:49 Device UPS: Main input bad. 0x01B0
    • 10/28/2015 04:00:49 Device UPS: On battery power in response to rapid change of input. 0x0109
  • switch back to main power
    • 10/28/2015 04:00:51 Device UPS: A backfeed relay fault exists. 0x016B
    • 10/28/2015 04:00:51 Device UPS: The output power is turned off. 0x0114
    • 10/28/2015 04:00:51 Device UPS: The graceful shutdown period has ended. 0x014F
    • 10/28/2015 04:00:51 Device UPS: No longer on battery power. 0x010A

I need to know under what circumstances the UPS produces and 00020 Error and why the smaller 2200 and 1500 UPS are not affected

  • undervoltage
  • overvoltage
  • ....

Many thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

0 Likes
0
8088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

A backfeed relay fault is supposed to indicate that the UPS' backfeed relay isn't behaving correctly. This relay disconnects the UPS from AC hot during a power failure, so the electricity generated by the UPS doesn't backfeed into mains or your generator. Backfeed protection is required so that circuits feeding the UPS can be de-energized and made safe for electrical work which would be difficult if the UPS kept it energized. The UPS detects if it doesn't open or close as it should.

As for why you're seeing the exact same fault on the replacement, that is really odd. I would call APC tech support, complain and ask about generator compatibility.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

maxfs79_apc
Crewman maxfs79_apc
Crewman

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

0 Likes
0
8088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

Dear Forum,

We have the same problem on UPS APC SRT8K. From diesel generator this is UPS work fine, but when we switch from generator to power line, sometimes UPS is turn off and print message "00020 Error and turned the output power off". On a web page in logs seems error: A backfeed relay fault exists.

In our UPS firmware 4.03. Can you please help me ?

Regards,

Maxim.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

0 Likes
0
8088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

Hi Maxim,

I just wrapped my related case up today. A firmware update on the unit itself solved the issue. Check to see if your ups is on firmware 4.4, if it isn't the instructions and files are in the link below. 

http://www.schneider-electric.us/sites/us/en/support/faq/faq_main.page?page=content&country=US〈=en&id=FA164737

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

0 Likes
0
8089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

A backfeed relay fault is supposed to indicate that the UPS' backfeed relay isn't behaving correctly. This relay disconnects the UPS from AC hot during a power failure, so the electricity generated by the UPS doesn't backfeed into mains or your generator. Backfeed protection is required so that circuits feeding the UPS can be de-energized and made safe for electrical work which would be difficult if the UPS kept it energized. The UPS detects if it doesn't open or close as it should.

As for why you're seeing the exact same fault on the replacement, that is really odd. I would call APC tech support, complain and ask about generator compatibility.

Reply

Link copied. Please paste this link to share this article on your social media post.

maxfs79_apc
Crewman maxfs79_apc
Crewman

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

0 Likes
0
8089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

Dear Forum,

We have the same problem on UPS APC SRT8K. From diesel generator this is UPS work fine, but when we switch from generator to power line, sometimes UPS is turn off and print message "00020 Error and turned the output power off". On a web page in logs seems error: A backfeed relay fault exists.

In our UPS firmware 4.03. Can you please help me ?

Regards,

Maxim.

Reply

Link copied. Please paste this link to share this article on your social media post.

mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

0 Likes
0
8088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

Hi Maxim,

I am actually currently working with another customer that has this issue on a srt10k. We replaced the ups and the same exact issue came back. They have other ups's that are not affected but are on a different panel. We are currently in the process of putting a power analyzer between the input of the ups and the upstream panel to see if there is anything that could be causing it on the power side. 

I will post back in this thread when we reach a resolution on it.

-Mike 

Reply

Link copied. Please paste this link to share this article on your social media post.

maxfs79_apc
Crewman maxfs79_apc
Crewman

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

0 Likes
0
8088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

Ok, thanks Mike.

Reply

Link copied. Please paste this link to share this article on your social media post.

maxfs79_apc
Crewman maxfs79_apc
Crewman

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

0 Likes
0
8088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

Hi Mike,

   Do you have any news about this issue ?

Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

mitsmith_apc
Lt. Commander mitsmith_apc
Lt. Commander

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

0 Likes
0
8089
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

Hi Maxim,

I just wrapped my related case up today. A firmware update on the unit itself solved the issue. Check to see if your ups is on firmware 4.4, if it isn't the instructions and files are in the link below. 

http://www.schneider-electric.us/sites/us/en/support/faq/faq_main.page?page=content&country=US〈=en&id=FA164737

Reply

Link copied. Please paste this link to share this article on your social media post.

maxfs79_apc
Crewman maxfs79_apc
Crewman

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

0 Likes
0
8088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:48 PM

Thank you for the answer, we try update firmware to 4.4, our UPS have 4.3.

I have one more question, how can I update firmware with no shutdown out power over NMS ?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:47 PM

0 Likes
0
8088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:45 AM . Last Modified: ‎2024-02-14 10:47 PM

Good day.
I had an error "00020 Error and turned the output power off". Current firmware UPS 04.4. The error only occurs when the load (10-15% load) is connected, if you disable input on the switch. After switching off the load, and turn on the switch input, the UPS switches to bypass, after 5-8 seconds the UPS is included in the normal mode.
UPS SRT10KRMXLI.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 02:46 AM . Last Modified: ‎2024-02-14 10:47 PM

0 Likes
0
8088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:46 AM . Last Modified: ‎2024-02-14 10:47 PM

Hi Michael, i did the firmware updating, but still have the same problem. Do you have another solution?

  • Tags:
  • 00020
  • error
  • power
  • sys
Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 02:46 AM . Last Modified: ‎2024-02-14 10:47 PM

0 Likes
0
8088
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 02:46 AM . Last Modified: ‎2024-02-14 10:47 PM

On 4/21/2017 8:31 PM, Mauro said:

Hi Michael, i did the firmware updating, but still have the same problem. Do you have another solution?

Hi Mauro,

I am experiencing the same issues. However we do not have a separate generator onsite. We're also on firmware 4.4

How was this fixed for you? 

Regards.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore