Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Resurrecting a SRT6KXLI with Error P.05

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Resurrecting a SRT6KXLI with Error P.05
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
CDSBP
Crewman CDSBP
Crewman

Posted: ‎2021-10-14 01:04 AM . Last Modified: ‎2022-10-19 01:22 AM

0 Likes
4
723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-10-14 01:04 AM . Last Modified: ‎2022-10-19 01:22 AM

Resurrecting a SRT6KXLI with Error P.05

Hi everyone, thanks in advance for all your help and ideas.

 

I am resurrecting a SRT6KXLI with dual APCRBC140 battery packs that was retired because of a constant Power Sys Error 00020 fault that has now been resolved by upgrading to the latest firmware, UPS 05.1 ID1013, per this post 

 

https://community.se.com/t5/Datacenter-Forum/SRT8KXLI-Power-Sys-Error-00020/td-p/287698

 

I am now getting the following errors:

P.05 contact customer support

Connect battery, backup not available

and Internal comm fault 154 in the logs 

 

I suspect that the battery packs are now beyond reviving and that the UPS is telling me to get new ones.  Before I go and throw a lot of cash at buying 2 new battery packs, can anyone share some insight into the P.05 and Fault 154 please?

 

Thank you

Labels
  • Labels:
  • Datacenter UPS
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
APC_Matt
Lieutenant JG APC_Matt Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-14 05:25 AM

0 Likes
2
716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-10-14 05:25 AM

Hi

 

Error 154 is a Lost comms event with the output on, and P.05 is a backfeed relay weld.

 

The only thing you can try to remedy these two issues is to 'braindead' the UPS,  removing the AC power and disconnecting the batteries to completely power the ups down and then reconnect. If that doesn't work the ups would need replacing

 

Regards

 

Matt

  • Tags:
  • english
Reply
CDSBP
Crewman CDSBP
Crewman

Posted: ‎2021-10-14 05:43 AM

In response to APC_Matt
0 Likes
1
714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-10-14 05:43 AM

Thannks Matt.  What constitutes a lost comms event please?  Could it be between PowerChute and my PC?

  • Tags:
  • english
Reply
APC_Matt
Lieutenant JG APC_Matt Lieutenant JG
Lieutenant JG

Posted: ‎2021-10-14 06:17 AM

In response to CDSBP
0 Likes
0
709
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-10-14 06:17 AM

Hi

In this case it's referencing a loss of communication on the internal communication buss rather than between the UPS and powerchute.

 

Matt

  • Tags:
  • english
Reply
CDSBP
Crewman CDSBP
Crewman

Posted: ‎2021-10-14 09:03 AM

0 Likes
0
700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-10-14 09:03 AM

Keeping this thread going in case anyone has had practical experience of how this relay issue was potentially resolved without an expensive APC repair please.  This is the second (of two) APC UPSes that has failed within 18 months of normal operating conditions, doesnt really inspire confidence in the brand, this unit being the warranty replacement for the first one that failed and is therefore out of  the original unit's 3 year warranty.

  • Tags:
  • english
Reply
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc