APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Posted: 2021-07-08 01:42 AM . Last Modified: 2024-02-29 10:36 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:42 AM . Last Modified: 2024-02-29 10:36 PM
Hi all,
I have inherited a couple of Smart UPS RT 3000 (I think - one's branded Dell and the other is unbranded) with AP9618 Network Management Cards (NMC) attached that were set up previously but is no record of username passwords (not apc/apc), IP addresses or MAC addresses and have uninstalled the PowerChute software as I can't get into it. I have found the MAC addresses and the IP's but cannot get the IP Configuration wizard to find them - I guess because they are already configured.
I have tried arp and ping to reset one of the cards to a different IP address on a VLAN tagged port on our switch, but cannot telnet onto the card to set it up. Running arp -a shows the MAC address with the IP address I set up with arp.
I have a couple of questions:
Thanks
Tony
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:42 AM . Last Modified: 2024-02-29 10:36 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:42 AM . Last Modified: 2024-02-29 10:36 PM
Thanks Bill, I'll give that a try.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:42 AM . Last Modified: 2024-02-29 10:36 PM
Tony,
On 9/21/2015 6:50 AM, Tony said:Will resetting the NMC affect the UPS i.e. turn it off and disrupt power to my production servers?
Resetting the NMC will not disrupt output.
On 9/21/2015 6:50 AM, Tony said:I have read that I can attach a cable (940-0024C) and access it through the local console. The cable I have has 2 D-SUB connectors, but cannot find a corresponding port on the NMC only one on the UPS itself. Where should I attach the cable to on the NMC?
You attach the 940-0024C cable to the serial port on the UPS. Using a terminal emulator (hyperterm, putty) the settings should be 2400bps, no parity, 8 data bits, 1 stop bit, and no flow control.
We have Kbase FA156075 "Network Management Card (NMC) Password Reset Procedure" that should help.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:42 AM . Last Modified: 2024-02-29 10:36 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-08 01:42 AM . Last Modified: 2024-02-29 10:36 PM
Thanks Bill, I'll give that a try.
Link copied. Please paste this link to share this article on your social media post.