APC9630 NMC2 installation

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC9630 NMC2 installation
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
9
3374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

APC9630 NMC2 installation

Hi Folks,

It's unclear from the installation docs whether or not this card is hot-pluggable ( well, the card is but...) is the unit?  I am looking to install it in a SMT3000 we recently purchased, does the unit need to be powered down or into something called bypass mode?? And if bypass mode, what effect does that have on the unit? Is it an "offline" event? In other words, do I need to power down any connected devices?

As always, many thanks in advance.

Buddy

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
0
3374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

Buddy,

The AP9630 is hot swappable. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
0
3375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

Buddy,

The AP9630 is hot swappable. 

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkC_apc
Commander MarkC_apc
Commander

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
0
3374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

Bill;

Does "hot swappable" mean that I can remove and re-install the APC963X cards when the green/amber lights are active on the card - under any condition of the UPS (on-line, on battery power, etc.) and any UPS model?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
0
3374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

Hi Buddy,

Yes, you may remove and reseat the APC963x cards while the UPS and the NMC is in any state.

Regards,

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
0
3374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

For reference, we have this question detailed here with technical details -> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA156132 

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
0
3374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

Thank you all, I've installed the card successfully. I've also run an ethernet cable from one of our core switches in order to set up and configure the card with an IP address, etc.

Would you happen to have a doc that explains this process? I seem to recall NOT to plug the console in on a "live" unit or bad things happen. Can I access the card over the network cable? I can't seem to locate the info for default ip and account ( apc/apc, perhaps?).

As always, thanks.

Buddy

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:42 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
0
3374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:42 AM . Last Modified: ‎2024-02-29 10:36 PM

Hi Buddy,

Our NMC2 TCP/IP settings setup information is in the user's guide but our knowledge base is a little more detailed here on set up -> http://www.schneider-electric.us/support/index?page=content&country=US〈=en&locale=en_US&id=FA156064 

You can connect both ethernet cable and console cable to the NMC2 while everything is running. I am not aware of any limitations on connecting either of these cables while a device is live, assuming you connect the appropriate serial cables. Connecting non-standard serial cables can cause a UPS, for example, to turn off because of the pinout. Other than that, I can't think of any other scenarios where I wouldn't recommend this.

NMC2's default to DHCP only by default using apc/apc so there is no default IP. So, if you have a DHCP server, you can maybe check its client list to figure out the IP address, knowing APC devices have a MAC that starts with 00 C0 B7. DHCP option 12 mentioned in the article above may also be an option for you. If you have a UPS with an LCD display, you may be able to find the IP within the advanced menu as well.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:42 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
0
3374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:42 AM . Last Modified: ‎2024-02-29 10:36 PM

Thanks again, Angela. We have DHCP configured on a separate subnet so I think moving the ethernet cable from the APC unit to that subnet will be easiest, let it get an IP via DHCP and then I can access it and configure. I can then bring it back once it's configured with the desired IP.

As always, thank you for the assistance.

Buddy

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:42 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
0
3374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:42 AM . Last Modified: ‎2024-02-29 10:36 PM

You're welcome! and I am sorry about Roethlisberger! wink

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:42 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
0
3374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:42 AM . Last Modified: ‎2024-02-29 10:36 PM

We get him back in 3 - 4 weeks, I'll bet. Could have been ALOT worse. Hopefully the dog whisperer will be able to help us out, we'll see.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore