Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
PowerChute Network Shutdown not logging events
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0801:41 AM. Last Modified: 2024-02-2910:36 PM
PowerChute Network Shutdown not logging events
Hi
I have recently installed Network Shutdown and connected to 3 UPS. During the initial startup of Network Shutdown it gets the events from all three UPS. After the first few minutes however it stops logging all events and never starts logging again. If I restart the service it starts logging again for a few minutes and again stops.
All devices are on the same network, no firewalls inbetween. I can access the web interface on all three UPS from the Network Shutdown server.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0801:41 AM. Last Modified: 2024-02-2910:36 PM
Hi,
PowerChute Network Shutdown receives data from the NMC on UDP port 3052. When PowerChute is started the port is open. Check to be sure the port remains open and that nothing is blocking packets.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0801:41 AM. Last Modified: 2024-02-2910:36 PM
Hi,
PowerChute Network Shutdown receives data from the NMC on UDP port 3052. When PowerChute is started the port is open. Check to be sure the port remains open and that nothing is blocking packets.