Power Chute Network Shutdown HELP PLEASE!!

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Power Chute Network Shutdown HELP PLEASE!!
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-08 01:40 AM . Last Modified: ‎2024-02-29 10:37 PM

0 Likes
7
2476
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:40 AM . Last Modified: ‎2024-02-29 10:37 PM

Power Chute Network Shutdown HELP PLEASE!!

I am trying to come up with a solution to gracefully shutdown my servers. i have 5 physical servers and 7 virtual using VMware ESXi. I want to use Power Chute Network Shutdown but I am a little confused on how to physically connect the servers and the UPS. It may be a stupid question but in the event of an outtage, how does the Server communicate with the UPS via Ethernet? Do I connect the Server and the UPS directly via an ethernet cable, or does the Ethernet cable from the UPS connect to a switch and that switch is connected to an UPS? 

Or does the Server know to shutdown once it has lost connectivity via ethernet with the UPS? I havent been able to find much information on this only the installation of Power Chute and configuring it. Any info on the actual physical connections and how they should communicate after a power outtage would be greatly appreciated!

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
0
2473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

Hi,

If you want environmental monitoring then you want the AP9631. If you do not want environmental monitoring then the AP9630 is the proper NMC. 

On 9/17/2015 2:11 PM, Bennett said:

Also, are they hot-swappable or do i have to turn off the UPS to install the NMC's?

Yes. The NMC are hot swappable. 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:40 AM . Last Modified: ‎2024-02-29 10:37 PM

0 Likes
0
2473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:40 AM . Last Modified: ‎2024-02-29 10:37 PM

Hi,

PowerChute Network Shutdown (PowerChute) works in conjunction with the UPS Network Management Card (NMC) to provide network-based shutdown of multiple computer systems. In the case of a UPS critical event, the software performs a graceful, unattended system shutdown before the UPS battery is exhausted. The number of protected systems is limited only by the capacity of the UPS. Each system running PowerChute needs to be connected to the network with valid IP v4 or IP v6 address and the NMC must be connected to the network with a valid IP v4 or IP v6 address. 

I recommend you read the PowerChute Brochure,  Application note 20 "Communication process for PowerChute Network Shutdown" and Application note 180 "PowerChute Network Shutdown for VMware"

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:40 AM . Last Modified: ‎2024-02-29 10:37 PM

0 Likes
0
2473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:40 AM . Last Modified: ‎2024-02-29 10:37 PM

Thanks for that, it helped a lot. I do have a question about how many Power Chute agents are recommended because of broadcast traffic. Does that mean limiting which servers have Power Chute installed. I have 2 ESXi hosts, so that would be 2 Power Chute agents, one installed on each ESXi host (i'm guessing). And then 5 more physical servers, so i would install 5 more Power Chute agents? Is that what i would be looking at or am i confused? Would that be too many agents. They are all connected to the same switch, so i am guessing i would only need to supply power to that one switch?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:37 PM

0 Likes
0
2473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:37 PM

Hi,

Yes. You need to install PowerChute Agent on each physical server. An example of a physical server is a Dell 3800 running Windows Server 2008 R2 or running VMware ESXi 5.5. You do not need to install PowerChute on the virtual machines (VMs) that are running on the ESXi hosts. 

The switch they are connected to needs to be powered by a UPS to prevent the loss of communications in the event of a power loss. When the NMC reports an event it sends single network packet. It does not send individual packet to each Agent so network traffic is minimal.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
0
2473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

Thanks, do i need to buy a certain edition or is that software free?

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
0
2473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

Hi,

For most locations PowerChute is free. I see from your profile you are in California so it is free to download at

http://www.apc.com/products/family/index.cfm?id=127

bqnmVf5XFCPfVMeXeFsDWg%3D%3D.pngbqnmVf5XFCPfVMeXeFsDWg%3D%3D.png

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
0
2473
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

One last question. Thanks for all your help.

I have 2 Smart UPS, SUA2200RM2U. I need to install Network Management Cards so i can start installing Power Chute. I was wondering if there are specific cards for my UPS or if any APC NMC will work? What would be a good choice for me since I have 7 servers connected to 2 different UPS? Also, are they hot-swappable or do i have to turn off the UPS to install the NMC's? Again, thanks for your help

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

0 Likes
0
2474
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 01:41 AM . Last Modified: ‎2024-02-29 10:36 PM

Hi,

If you want environmental monitoring then you want the AP9631. If you do not want environmental monitoring then the AP9630 is the proper NMC. 

On 9/17/2015 2:11 PM, Bennett said:

Also, are they hot-swappable or do i have to turn off the UPS to install the NMC's?

Yes. The NMC are hot swappable. 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore