Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Replaced Batteries, No Time Remaining Improvement
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2810:28 AM. Last Modified: 2024-03-1505:53 AM
Replaced Batteries, No Time Remaining Improvement
I have a fairly ancient SU2200INET. I last replaced the batteries about 4 years ago, but my current monitoring logs only go back to December. Even from those, something strange has been happening with the battery capacity in terms of Wh. The UPS doesn't report this directly - I am inferring it from the following two values reported by the UPS:
1) LOADPCT (% load, assumed to be % of 1600W maximum rated output)
2) TIMELEFT (seconds left with current load on current battery charge)
From these two, I work out the battery capacity.
I can see that 8 months ago, it was about 280Wh. In that time there have been two calibrations and maybe 3-4 power outages, and the battery capacity now is showing 42Wh. The self tests pass, and the UPS says the batteries are OK.
I also recently acquired a much newer SUA3000I and with the same batteries (different connector but identical batteries), and that is showing close to 400Wh battery capacity after calibrating.
So I figured the battery capacity is expected to be about 400Wh, and with my old batteries being down to 42Wh, means that they are down to barely 10% of their capacity and it's time to replace them. Yet the UPS was saying they are fine. Is that sane/normal, especially since the UPS doesn't show the battery capacity directly, and I have to infer it from the two values mentioned?
I just got replacement batteries, fitted them, recalibrated - and they are also whosing 42Wh capacity. How is that possible? The load on the UPS hasn't changed in the past year, yet the battery endurance is showing as far shorter than before and new batteries haven't resolved the problem. How is that possible? Why have new batteries not restored the time on battery I had before on a new battery pack?