Reboot Network Management Card after DHCP Request Failure

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Reboot Network Management Card after DHCP Request Failure
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:35 AM . Last Modified: ‎2024-03-05 02:07 AM

0 Likes
8
1900
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:35 AM . Last Modified: ‎2024-03-05 02:07 AM

Reboot Network Management Card after DHCP Request Failure

Hi all.  I have about 12 network management cards I changed over to DHCP Only and selected to only do 3 dhcp attempts.  Thinking it wouldn't be an issue, the actual DHCP scope or vlan was not setup at the time I set the NMC to DHCP Only.

Now the DCHP scope and vlan are all configured correctly.  However, in order for the NMC to receive an IP address, I have to console into the card and set it to DHCP again but with the 0 retries (infinite).

According to the built-in help "If a DHCP timeout/failure occurs, the Card will stop requesting network assignment until it is rebooted."

So, given some cards are at remote locations driving distance away, is it possible to reboot the NMC without having to physically be at the UPS?  So far I've tried shutdown/ no shutdown of the switch port a NMC connects to, but still no IP address is being pulled.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:35 AM . Last Modified: ‎2024-03-05 02:07 AM

0 Likes
0
1901
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:35 AM . Last Modified: ‎2024-03-05 02:07 AM

I am having this same issue with several cards at remote sites. In one location, I have been able to confirm that the Network Management Card is not sending out a DHCP request, and the IP address defaults to 0.0.0.0. That leads me to two questions:

  1. Is there anyway to remotely reset a device if it does not have an IP?
  2. Is there a way to change the setting so that the NMC continues to retry DHCP requests indefinitely? 

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:35 AM . Last Modified: ‎2024-03-05 02:07 AM

0 Likes
0
1901
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:35 AM . Last Modified: ‎2024-03-05 02:07 AM

What model cards are these? FYI, for our v6.0.6 and higher of Network Management Card 2 devices, we removed DHCP retries as an option.

Anyway, two ideas we came up with here were:

  • If you can access a machine locally/on the same segment as the card, set your ARP cache with the mac of the NMC, then ping with the 117 size payload as outlined in our ARP set up instructions here -> How do you make a Network Management Card communicate on a network? | FAQs | Schneider Electric US
  • Try to keep the switch port off for at least 10 minutes. We have a failsafe watchdog built in that if the card does not see network traffic for 10 minutes that it will reboot in an attempt to fix it's interface. This may require valid network settings already to be there but I am not 100% sure.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 04:35 AM . Last Modified: ‎2024-03-05 02:07 AM

0 Likes
0
1902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 04:35 AM . Last Modified: ‎2024-03-05 02:07 AM

I am having this same issue with several cards at remote sites. In one location, I have been able to confirm that the Network Management Card is not sending out a DHCP request, and the IP address defaults to 0.0.0.0. That leads me to two questions:

  1. Is there anyway to remotely reset a device if it does not have an IP?
  2. Is there a way to change the setting so that the NMC continues to retry DHCP requests indefinitely? 
Reply

Link copied. Please paste this link to share this article on your social media post.

josephcoombe
josephcoombe
Cadet

Posted: ‎2025-07-03 01:11 PM

0 Likes
3
877
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-03 01:11 PM

We are also experiencing this issue. Creates a huge headache b/c a person then has to physically reset NMC card.

>Try to keep the switch port off for at least 10 minutes. We have a failsafe watchdog built in that if the card does not see network traffic for 10 minutes that it will reboot in an attempt to fix it's interface. 


Do NMC2, NMC3, and NMC4 cards all have this behavior? 

>This may require valid network settings already to be there but I am not 100% sure

Is there an official statement on this from Schneider?

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-07-07 12:36 AM

In response to josephcoombe
0 Likes
2
876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-07 12:36 AM

All of the NMC you listed has a watchdog timer which you can review on page 9:

https://download.schneider-electric.com/files?p_enDocType=User+guide&p_File_Name=990-3402R-EN.pdf&p_...

 

DHCP: See page 49-51 as it relates to this topic and the available options.

 

Questions Ask . .  đź‘Ť

Reply

Link copied. Please paste this link to share this article on your social media post.

josephcoombe
josephcoombe
Cadet

Posted: ‎2025-07-08 07:50 AM

In response to Teken
0 Likes
1
824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-08 07:50 AM

Thank you - that answers my question.

Followup question about
>If a DHCP server is found, but the request to that server does not work or times out, it stops requesting network settings until it is restarted."
page 51

What if a DHCP server is NOT found? Will a NMC continue to broadcast DORA discover messages indefinitely or is there a timeout?


Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-07-09 03:03 AM

In response to josephcoombe
0 Likes
0
820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-09 03:03 AM

The watch dog timer is set to 9.5 minutes as such would expect the NMC to try again for a period of time. 

You’ll need to use wire shark or something to monitor what behaviour is seen. There are countless scenarios and how the system is set up that can impact how the system functions and behaves.

 

As a starter what firmware is on the NMC. How the network infrastructure handles port flapping. 

You’re looking for TX (Transmit) packets not RX packets. As such if the the NMC is defined and monitored by a NMS (SNMP) or ping alive etc activity will be seen.

 

Wire Shark or similar tools will offer a more definitive answer. 

Questions Ask . . . 

Reply

Link copied. Please paste this link to share this article on your social media post.

josephcoombe
josephcoombe
Cadet

Posted: ‎2025-07-15 01:03 PM

0 Likes
1
758
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-15 01:03 PM

We're doing testing with NMC3 and NMC4 cards to validate reports that the cards appear to timeout and stop polling for DHCP if no DHCP server is available. This is different from other devices in network stack that poll for DHCP indefinitely until a server becomes available.

What we need to understand from Schneider is what the expected behavior should be (e.g. for latest firmware release on NMC3 / NMC4).

Specifically, if a NMC is powered on and begins to broadcast DORA discover messages and no DHCP server replies with an offer message, will the NMC timeout and stop broadcasting discover messages 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: ‎2025-07-16 01:56 AM

In response to josephcoombe
0 Likes
0
755
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2025-07-16 01:56 AM

You should contact APC Technical Support for a more definitive answer and compare what you see in the field and report back your findings here.

 

Questions Ask . . . 👍

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore