This unit does not have the correct 20A plug(1 horizontal blade on plug) on it. Is it safe to use a 20A to 15A plug converter on this or will the server draw too much amperage?
Could this damage the battery / server or just result in less runtime?
Thanks in advance...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:09 PM . Last Modified: 2024-03-14 11:25 PM
you can use the same principles mentioned in [this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=184].
you will be limited by the capacity of the UPS itself. it will overload based on the specs it can handle - 500 Watts or 750 VA.
i think you will be fine. it will have no effect on the UPS you just need to make sure that the UPS is sized appropriately for the amount of wattage your piece of equipment requires. this will not affect the runtime of the UPS or anything.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:09 PM . Last Modified: 2024-03-14 11:25 PM
you can use the same principles mentioned in [this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=184].
you will be limited by the capacity of the UPS itself. it will overload based on the specs it can handle - 500 Watts or 750 VA.
i think you will be fine. it will have no effect on the UPS you just need to make sure that the UPS is sized appropriately for the amount of wattage your piece of equipment requires. this will not affect the runtime of the UPS or anything.