Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-28 10:09 PM . Last Modified: 2024-03-14 11:25 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:09 PM . Last Modified: 2024-03-14 11:25 PM
We have a 3-Phase MGE UPS (20kVA). Currently our phases are unbalanced. I'm not familiar with the calculations that effect unbalanced loads in 3-Phase systems, and I'm wondering what effects an unbalanced load is actually having on our total system.
By balancing the loads would the entire system become more efficient? Would it increase battery life? etc. etc.
Thanks for your help.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:10 PM . Last Modified: 2024-03-14 11:25 PM
hi
the MGE unit has to have each phase within 10amps of each other, otherwise the system could go into bypass, so because of this balancing is very important. Balancing the load also helps with efficiency but has no effect on the batteries
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 10:10 PM . Last Modified: 2024-03-14 11:25 PM
hi
the MGE unit has to have each phase within 10amps of each other, otherwise the system could go into bypass, so because of this balancing is very important. Balancing the load also helps with efficiency but has no effect on the batteries
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.