Want to shut down servers with % of battery left, not X amount of time left

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Want to shut down servers with % of battery left, not X amount of time left
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
109
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Mgregory2K_apc
Ensign Mgregory2K_apc
Ensign

Posted: ‎2021-06-28 10:10 PM . Last Modified: ‎2024-03-14 11:25 PM

0 Likes
4
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:10 PM . Last Modified: ‎2024-03-14 11:25 PM

Want to shut down servers with % of battery left, not X amount of time left

I have a Symmetra PX model #: SYCF40KF

I have installed PCNS v2.2 on all of our servers (about 15) and I have configured it to shut down after X amount of time - depending on if the server is production or not. We recently had a power outage and the batteries ran out of juice long before the time I had specified for production equipment to shut down.

I have been told that I should be able to configure it to shut down when the batteries are at a certain level of charge. For example, if I wanted to shut down production servers when there is 15% of battery life left in our UPS.

However, I called APC and they have told me that this is not possible. So, my question is this: Is it possible to use PCNS to shut down in this way? If not, is there another product that I could use? This is a pretty critical issue because I live in an area where power outages are relatively common.

Also, I had to copy the config file over to each server individually and I've been told that I should be able to centrally configure each device. I'm pretty new to PCNS so any info would be very helpful.

Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • 2003
  • battery
  • life
  • network
  • pcns
  • percentage
  • server
  • shutdown
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 10:10 PM . Last Modified: ‎2024-03-14 11:25 PM

0 Likes
0
1404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:10 PM . Last Modified: ‎2024-03-14 11:25 PM

Expanding on what i Picked a Winna said,

Lets say you have servers A, B, and C, and you want A to shutdown first. Once we've signaled A to shut down, the UPS will need to turn off and on the power to get A to turn back on again. However, to safely do that, B and C need to shut down as well. So in short, if you shut down one of them, you need to shut down all of them. Hence, why you set up the shut down time for all three on the NMC rather than per-server.

By using the PCNS settings, you can delay the shutdowns for B and C so that they start a certain time after the signal to shutdown, thereby staggering them. The NMC keeps track of this and will not reboot the UPS until enough time has past that all PCNS clients should have shutdown.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 10:10 PM . Last Modified: ‎2024-03-14 11:25 PM

0 Likes
0
1406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:10 PM . Last Modified: ‎2024-03-14 11:25 PM

On your NMC under UPS -> Configuration -> Shutdown, there's a "Low Battery Duration" setting. For example, if you set it for 5 minutes, then 5 minutes before the batteries die, your computers should begin a shutdown.

Reply

Link copied. Please paste this link to share this article on your social media post.

Mgregory2K_apc
Ensign Mgregory2K_apc
Ensign

Posted: ‎2021-06-28 10:10 PM . Last Modified: ‎2024-03-14 11:25 PM

0 Likes
0
1406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:10 PM . Last Modified: ‎2024-03-14 11:25 PM

Thanks! I was expecting it to be on the server side and not the NMC

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:10 PM . Last Modified: ‎2024-03-14 11:25 PM

0 Likes
0
1406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:10 PM . Last Modified: ‎2024-03-14 11:25 PM

you can do it a couple different ways. if you want all your servers to shutdown at the same point, voidstar's suggestion is the way to go.

if you wanted to stagger shutdowns, there are configuration changes you can make on the powerchute software on the servers.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-28 10:10 PM . Last Modified: ‎2024-03-14 11:25 PM

0 Likes
0
1405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:10 PM . Last Modified: ‎2024-03-14 11:25 PM

Expanding on what i Picked a Winna said,

Lets say you have servers A, B, and C, and you want A to shutdown first. Once we've signaled A to shut down, the UPS will need to turn off and on the power to get A to turn back on again. However, to safely do that, B and C need to shut down as well. So in short, if you shut down one of them, you need to shut down all of them. Hence, why you set up the shut down time for all three on the NMC rather than per-server.

By using the PCNS settings, you can delay the shutdowns for B and C so that they start a certain time after the signal to shutdown, thereby staggering them. The NMC keeps track of this and will not reboot the UPS until enough time has past that all PCNS clients should have shutdown.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of