set up Smart UPS SUA1500 and new computer with Powerchute and cables

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • set up Smart UPS SUA1500 and new computer with Powerchute and cables
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
pmg435T_apc
pmg435T_apc
Cadet

Posted: ‎2021-06-28 10:09 PM . Last Modified: ‎2024-03-14 11:25 PM

0 Likes
3
1335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:09 PM . Last Modified: ‎2024-03-14 11:25 PM

set up Smart UPS SUA1500 and new computer with Powerchute and cables

I have my new personal computer, 24" LCD monitor, DSL modem, WiFi route and external backup hard drive plugged in to the SUA1500. I understand I only can use the Powerchute Business Edition software with the SUA1500. As a senior citizen and mostly beginner with computers I want to keep things simple. Sorry, but I have a lot of (perhaps dumb) questions.

1. The OS on my pc is Vista SP1 Home Premium 64-bit edition (I never used Vista before). The compatibility chart for PCBE only lists Vista Business/Enterprise/Ultimate. Will PCBE still function with 64-bit Vista Home Premium?

2. My pc only has USB connectors. Can I use the USB on the SUA to my pc without loss of functionality of PCBE or do I need to use the DB-9 serial connector on the UPS for full functionality?

3. In another thread I read about intermittent loss of communications when using the USB to USB connection. Do I need to use a DB-9 to USB connecting cable to prevent that problem? And does APC sell such a cable? Any other gotcha's when using this kind of setup if recommended? Or should I just stay away from this setup?

4. I know that the DB-9 cable is a special APC cable. Is that also true for the USB to USB cable or can any generic USB cable be used?

5. Since I have only my pc connected to the UPS (no server or other pc's), do I still need to install the agent, server and console components of PCBE or is the agent sufficient for all functionality to monitor and control the UPS? Or can I use only the agent and console components? What would be easier to use for a beginner like me?

6. On AC power loss, I should be able to set up the UPS to have my pc do a controlled shutdown. Once that is done, will the UPS run down its batteries until power is restored or does the UPS shut itself down to conserve its batteries?

7. I have Norton Internet Security 2009 running on my pc. What do I need to do with NIS2009 when I install PCBE? Any other problems with security software and PCBE?

I am sure that I will have lots more questions once I have PCBE loaded to my computer.
I want to thank in advance all who will provide answers to these questions.

Paul

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • PowerChute
  • smart-ups
  • usb
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:09 PM . Last Modified: ‎2024-03-14 11:25 PM

0 Likes
0
1335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:09 PM . Last Modified: ‎2024-03-14 11:25 PM

i will try to answer the questions to the best of my knowledge..

I have my new personal computer, 24" LCD monitor, DSL modem, WiFi route and external backup hard drive plugged in to the SUA1500. I understand I only can use the Powerchute Business Edition software with the SUA1500. As a senior citizen and mostly beginner with computers I want to keep things simple. Sorry, but I have a lot of (perhaps dumb) questions.
1. The OS on my pc is Vista SP1 Home Premium 64-bit edition (I never used Vista before). The compatibility chart for PCBE only lists Vista Business/Enterprise/Ultimate. Will PCBE still function with 64-bit Vista Home Premium?
*Any version of Windows Vista 64 bit should work fine with PCBE 8.0.1.*
2. My pc only has USB connectors. Can I use the USB on the SUA to my pc without loss of functionality of PCBE or do I need to use the DB-9 serial connector on the UPS for full functionality?
*The only loss of functionality that you will get is mentioned in [this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8022]. you will see just the input and output voltage, not min and max values. other than that, all of the same functionality is there.*
3. In another thread I read about intermittent loss of communications when using the USB to USB connection. Do I need to use a DB-9 to USB connecting cable to prevent that problem? And does APC sell such a cable? Any other gotcha's when using this kind of setup if recommended? Or should I just stay away from this setup?
*There have been cases of intermittent USB communication loss. A good portion of the time, it relates to something on the computer - perhaps USB ports being powered off in standby or hibernate, using a USB hub, etc so APC can work with you to narrow those types of things down before determining that there is a USB issue with the Smart UPS itself. After this has been proved, APC does have a cable that can be provided to you if the UPS is indeed the cause of the issue. I would recommend just starting off with USB. it should work fine.*
4. I know that the DB-9 cable is a special APC cable. Is that also true for the USB to USB cable or can any generic USB cable be used?
*the UPS ships with all the cables needed. some Smart UPS use a special RJ-45 to USB cable and some use a standard USB A->USB B type of cable. I believe this one uses a standard A to B cable but it will also include one - no need to buy extra cables.*
5. Since I have only my pc connected to the UPS (no server or other pc's), do I still need to install the agent, server and console components of PCBE or is the agent sufficient for all functionality to monitor and control the UPS? Or can I use only the agent and console components? What would be easier to use for a beginner like me?
*You will get a CD that just includes the Agent software and thats all you need to use. The server and console portions of PCBE are now included in a paid version of PCBE for users with more than one UPS. The Agent is a web service that runs so you just type http://127.0.0.1:3052 in your web browser or alternatively http://IP of your computer:3052 and you will be able to bring up the web page with the settings to adjust/UPS status, etc*
6. On AC power loss, I should be able to set up the UPS to have my pc do a controlled shutdown. Once that is done, will the UPS run down its batteries until power is restored or does the UPS shut itself down to conserve its batteries?
*You can do it either way. There are settings you can change to have the computer shutdown immediately or when the battery runs out or even after the UPS has been on battery for 5 minutes or something. Shutdown for both the UPS and PC is very flexible.*
7. I have Norton Internet Security 2009 running on my pc. What do I need to do with NIS2009 when I install PCBE? Any other problems with security software and PCBE?
*I havent seen any issues with this. It may not let you access the web browser portion of the interface but you could add the loopback address (127.0.0.1) to your trusted sites in the web browser but i am not aware of any problems installing the software with Norton.*


hope this helps!!

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:09 PM . Last Modified: ‎2024-03-14 11:25 PM

0 Likes
0
1335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:09 PM . Last Modified: ‎2024-03-14 11:25 PM

no problem. yes you can grab all of that stuff from the website besides the cable.

Reply

Link copied. Please paste this link to share this article on your social media post.

pmg435T_apc
pmg435T_apc
Cadet

Posted: ‎2021-06-28 10:09 PM . Last Modified: ‎2024-03-14 11:25 PM

0 Likes
0
1335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:09 PM . Last Modified: ‎2024-03-14 11:25 PM

Hello i picKed a winna,

Thank you for answering all my questions. It seems that I worry too much before I really need to, probably because I am new to this. If I do run into problems I will re-visit the site.

As far as the included CD and cables, I don't have them because I tried to save some money by getting a refurbished UPS unit from CBM that comes without any of those accessories. I should be able to pick up a standard A to B USB cable in an electronics store and connect directly to an USB port on my computer. And I believe I can download the required software from the APC website. If I have intermittent communication problems with the USB cable I do not think I can qualify for APC support. So I hope I will be OK.

Once again, thank you.
Paul

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 10:09 PM . Last Modified: ‎2024-03-14 11:25 PM

0 Likes
0
1336
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 10:09 PM . Last Modified: ‎2024-03-14 11:25 PM

i will try to answer the questions to the best of my knowledge..

I have my new personal computer, 24" LCD monitor, DSL modem, WiFi route and external backup hard drive plugged in to the SUA1500. I understand I only can use the Powerchute Business Edition software with the SUA1500. As a senior citizen and mostly beginner with computers I want to keep things simple. Sorry, but I have a lot of (perhaps dumb) questions.
1. The OS on my pc is Vista SP1 Home Premium 64-bit edition (I never used Vista before). The compatibility chart for PCBE only lists Vista Business/Enterprise/Ultimate. Will PCBE still function with 64-bit Vista Home Premium?
*Any version of Windows Vista 64 bit should work fine with PCBE 8.0.1.*
2. My pc only has USB connectors. Can I use the USB on the SUA to my pc without loss of functionality of PCBE or do I need to use the DB-9 serial connector on the UPS for full functionality?
*The only loss of functionality that you will get is mentioned in [this article|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=8022]. you will see just the input and output voltage, not min and max values. other than that, all of the same functionality is there.*
3. In another thread I read about intermittent loss of communications when using the USB to USB connection. Do I need to use a DB-9 to USB connecting cable to prevent that problem? And does APC sell such a cable? Any other gotcha's when using this kind of setup if recommended? Or should I just stay away from this setup?
*There have been cases of intermittent USB communication loss. A good portion of the time, it relates to something on the computer - perhaps USB ports being powered off in standby or hibernate, using a USB hub, etc so APC can work with you to narrow those types of things down before determining that there is a USB issue with the Smart UPS itself. After this has been proved, APC does have a cable that can be provided to you if the UPS is indeed the cause of the issue. I would recommend just starting off with USB. it should work fine.*
4. I know that the DB-9 cable is a special APC cable. Is that also true for the USB to USB cable or can any generic USB cable be used?
*the UPS ships with all the cables needed. some Smart UPS use a special RJ-45 to USB cable and some use a standard USB A->USB B type of cable. I believe this one uses a standard A to B cable but it will also include one - no need to buy extra cables.*
5. Since I have only my pc connected to the UPS (no server or other pc's), do I still need to install the agent, server and console components of PCBE or is the agent sufficient for all functionality to monitor and control the UPS? Or can I use only the agent and console components? What would be easier to use for a beginner like me?
*You will get a CD that just includes the Agent software and thats all you need to use. The server and console portions of PCBE are now included in a paid version of PCBE for users with more than one UPS. The Agent is a web service that runs so you just type http://127.0.0.1:3052 in your web browser or alternatively http://IP of your computer:3052 and you will be able to bring up the web page with the settings to adjust/UPS status, etc*
6. On AC power loss, I should be able to set up the UPS to have my pc do a controlled shutdown. Once that is done, will the UPS run down its batteries until power is restored or does the UPS shut itself down to conserve its batteries?
*You can do it either way. There are settings you can change to have the computer shutdown immediately or when the battery runs out or even after the UPS has been on battery for 5 minutes or something. Shutdown for both the UPS and PC is very flexible.*
7. I have Norton Internet Security 2009 running on my pc. What do I need to do with NIS2009 when I install PCBE? Any other problems with security software and PCBE?
*I havent seen any issues with this. It may not let you access the web browser portion of the interface but you could add the loopback address (127.0.0.1) to your trusted sites in the web browser but i am not aware of any problems installing the software with Norton.*


hope this helps!!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore