Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Powerchute Network shutdown broadcast Query
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2809:23 PM. Last Modified: 2024-03-1512:33 AM
Powerchute Network shutdown broadcast Query
Hi,
Please can someone tell me if the broadcast element of Powerchute Network Shutdown only affects computers that are registered to one network management card? i.e. I have three APC UPS devices, one in each server room. The servers in each server room are on the same subnet. I am concerned that a shutdown command from a ups on the 3rd floor will trigger the shutdown of servers located on the 6th, which has a different IP address but on the same subnet.
Thanks
Martin
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2809:23 PM. Last Modified: 2024-03-1512:33 AM
there wont a be a problem. the management card only will only sent unicasts for shutting down to those clients that are listed as Powerchute Network Shutdown clients on any particular management card.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2809:23 PM. Last Modified: 2024-03-1512:33 AM
there wont a be a problem. the management card only will only sent unicasts for shutting down to those clients that are listed as Powerchute Network Shutdown clients on any particular management card.