Powerchute Network shutdown broadcast Query
Hi,
Please can someone tell me if the broadcast element of Powerchute Network Shutdown only affects computers that are registered to one network management card? i.e. I have three APC UPS devices, one in each server room. The servers in each server room are on the same subnet. I am concerned that a shutdown command from a ups on the 3rd floor will trigger the shutdown of servers located on the 6th, which has a different IP address but on the same subnet.
Thanks
Martin
- Labels:
-
Smart-UPS & Symmetra LX | RM
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:23 PM . Last Modified: 2024-03-15 12:33 AM
there wont a be a problem. the management card only will only sent unicasts for shutting down to those clients that are listed as Powerchute Network Shutdown clients on any particular management card.
[here is a link to an article that may help you understand a little more how this process works too|http://www.apcmedia.com/salestools/BKIR-6QWKC5_R0_EN.pdf]
i realize you arent connecting more than 50 computers but it explains how this stuff works like the broadcasts and all that.
hope this helps!
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 09:23 PM . Last Modified: 2024-03-15 12:33 AM
there wont a be a problem. the management card only will only sent unicasts for shutting down to those clients that are listed as Powerchute Network Shutdown clients on any particular management card.
[here is a link to an article that may help you understand a little more how this process works too|http://www.apcmedia.com/salestools/BKIR-6QWKC5_R0_EN.pdf]
i realize you arent connecting more than 50 computers but it explains how this stuff works like the broadcasts and all that.
hope this helps!