Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

UPS with generator

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • UPS with generator
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:34 AM

0 Likes
8
1052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:34 AM

UPS with generator

Hi folks,

I got a new Petrol Generator. I'm trying to connect to to my UPS systems in my house. The generator is supposed to have an AVR in it...

I have 4 UPS in the house. 2 are the step approximated type (one tower style and one rack style), 2 are the pure sine wave type (one tower style and one rack style).

Depending on how much I load the generator, some of the UPS's will constantly flick between battery and power..

However, one of my pure sine wave rack units hasn't caused any problems at all (stays on generator power constatly)

Any ideas?

Thanks

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

0 Likes
0
1052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

thanks for your help.

my next question is a little off topic. With my generator, my lights flicker a bit. Would something like the APC Line-R help this?

I have a feeling that this generator has a crappy AVR in it...

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:34 AM

0 Likes
0
1052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:34 AM

the only thing you can do in this situation is really lower the sensitivity on the unit if available. you can do this on standby UPSs (step approx sine wave) as well as line interactive UPSs. if you have a double online conversion UPS, it doesnt have a sensitivity setting due to its topology.

if the voltage/frequency is out of range, and lowering the sensitivity doesnt help, the only thing to do would be to clean up the power on the generator end.

if you can tell me a little bit more about specific models you have, i can tell you how to change the sensitivity if you dont have the software available.

on most Smart UPS (line interactive), you can change the sensitivity on the UPSs on the back via a little LED/switch. on certain Back UPSs, you can change it via the front switch with the UPS off. I can elaborate on that though if you need help depending on the models you have.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

0 Likes
0
1052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

thanks for your reply.

I did some searching online and came to the conclusion as yourself.

I have:

2 X Smart-UPS (These are my 2 pure sine wave ones)
1 X Back-UPS CS 650
1 X Powerstack 450

I have found how to change the sensitivity on the first 3 but have no idea on the powerstack.

Cheers

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

0 Likes
0
1052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

hmm..

[found the manual here|http://www.apcmedia.com/salestools/ASTE-6Z8L9U_R0_EN.pdf] but it didnt mention it either. i am assuming you'd need to do it through the software since it doesnt have the button on the back.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

0 Likes
0
1052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

Just another note, is it bad for the servers to run them off my noisey generator. My generator has an AVR in it however obviously it's still a very crappy waveform..

Is there such a thing that can protect the servers' PSUs from being damaged? (Something like a noise filter maybe)?

Thanks

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

0 Likes
0
1052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

the UPS should not pass through anything that is THAT bad. if anything, it will go on battery still if the power is not acceptable.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

0 Likes
0
1052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

yes, it wouldnt let anything really bad get through that is outside of the tech specs on the webpage for the UPS.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

0 Likes
0
1052
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

Even if they are all on low sensitivity?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

0 Likes
0
1053
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 09:23 PM . Last Modified: ‎2024-03-15 12:33 AM

thanks for your help.

my next question is a little off topic. With my generator, my lights flicker a bit. Would something like the APC Line-R help this?

I have a feeling that this generator has a crappy AVR in it...

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of