PowerChute network shutdown and power failure simulation
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2806:08 AM. Last Modified: 2024-03-1802:43 AM
PowerChute network shutdown and power failure simulation
Hello, I realize the reconfiguration of a Smart-ups 5000 with a management card AP9630 (with sumx 6.4.6) and powerchute network shutdown.I added a test agent and I would like to simulate a power failure to verify that the powerchute configuration is operational before adding other agents.
Is there a way to do this simulation without disrupting the rest of the diet?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2806:08 AM. Last Modified: 2024-03-1802:43 AM
Hi,
To test the system you could configure a lost communication event between the NMC/UPS. Do not select turn off UPS and then remove the network connection between the PowerChute client and the NMC/UPS. When PowerChute see that communication has been lost it will power down the OS but will not power down the UPS.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-2806:08 AM. Last Modified: 2024-03-1802:43 AM
Hi,
To test the system you could configure a lost communication event between the NMC/UPS. Do not select turn off UPS and then remove the network connection between the PowerChute client and the NMC/UPS. When PowerChute see that communication has been lost it will power down the OS but will not power down the UPS.