Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
Hello,
i have two SRT 2200 XLI, and both have the the same failure "charger low voltage" event code 142.
both have been repaired due to fan failures within 4 month.
when i got them back one started directly with mentioned error. but was just once a day now both UPS's have the same error plugged or on plugged in the wall. one error after the other, all event code 142
i looked around but couldn't find event code 142.
is this a setting i can adjust or is the charger toast and need to be replaced ?
batteries are still good indicated by the ups
thanks in advance
Arjen Hoekman
Lima
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
Hello -
This event usually indicates a blown fuse in the charger of the UPS. I would suggest contacting your local technical support group for further assistance and/or getting a replacement unit under warranty. This fuse is not field serviceable.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
thanks Liam, ill contact the local team