PowerChute network shutdown and power failure simulation
Hello, I realize the reconfiguration of a Smart-ups 5000 with a management card AP9630 (with sumx 6.4.6) and powerchute network shutdown. I added a test agent and I would like to simulate a power failure to verify that the powerchute configuration is operational before adding other agents.
Is there a way to do this simulation without disrupting the rest of the diet?
Thank you in advance.
Philippe
- Labels:
-
Smart-UPS & Symmetra LX | RM
- Tags:
- failure
- PowerChute
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
Hi,
To test the system you could configure a lost communication event between the NMC/UPS. Do not select turn off UPS and then remove the network connection between the PowerChute client and the NMC/UPS. When PowerChute see that communication has been lost it will power down the OS but will not power down the UPS.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:08 AM . Last Modified: 2024-03-18 02:43 AM
Hi,
To test the system you could configure a lost communication event between the NMC/UPS. Do not select turn off UPS and then remove the network connection between the PowerChute client and the NMC/UPS. When PowerChute see that communication has been lost it will power down the OS but will not power down the UPS.
Link copied. Please paste this link to share this article on your social media post.