Power supply with Power factor correction causing issues

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Power supply with Power factor correction causing issues
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
Teken
Spock Teken
111
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:33 PM . Last Modified: ‎2024-03-15 03:56 AM

0 Likes
4
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:33 PM . Last Modified: ‎2024-03-15 03:56 AM

Power supply with Power factor correction causing issues

Hello everyone! I recently deployed an HP ProLiant ML150 that and installed an APC Smart-UPS SC 1500. When the devices flips to battery power, the Overload light flashes twice (repeatedly) and emits a loud beep/buzz sound. The SC has only the server and a 15" LCD display plugged into it; and Powerchute indicates that it has only 25% load.

After speaking with Support, they told me that servers that have Power Factor Corrected power supply's are not compatible with the SC 1500 despite my failed attempts to locate this piece of information in any of APC's documentation. Has anyone else heard/experienced this issue? Does the power factor corrected answer make sense to anyone?

Thanks in advance!
Sean

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
  • Tags:
  • power_factor_correction
  • smart-ups_sc_1500
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:33 PM . Last Modified: ‎2024-03-15 03:56 AM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:33 PM . Last Modified: ‎2024-03-15 03:56 AM

Have you tried another server of the same type, another server that you know has a PFC power supply, even another power supply in the server? If could, possibly, be the power supply not a PFC problem.

If all fails see if your friendly APC Rep will agree to swap it out for one that is compatible.

Regards
Alan G

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Anonymous user
Not applicable

Posted: ‎2021-06-28 06:33 PM . Last Modified: ‎2024-03-15 03:56 AM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:33 PM . Last Modified: ‎2024-03-15 03:56 AM

Here's an interesting update -- I went to APC's sizing utility on their website (http://www.apc.com/sizing) and filled out their wizard/form using the server I installed as the example server; and they told me to purchase the SC 1500 - so now I am totally confused.

Thanks in advance for anyone's assistance with this issue.


Sean

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:33 PM . Last Modified: ‎2024-03-15 03:56 AM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:33 PM . Last Modified: ‎2024-03-15 03:56 AM

Yep. That's just the way it is sometimes. The only way around is to get a sinewave UPS.

Make sure it's not a battery related issue first. Disconnect everything, then plug in a 500W to 600W load, such as a halogen work light or a small heater based appliance with current rating of about 5A. The UPS should support the heater or light bulb when switched over to battery.

If you pass this, but it won't work with your computer, you have a power suply-UPS interaction.

Try an SU1000NET or SU1400NET in that case.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-28 06:33 PM . Last Modified: ‎2024-03-15 03:56 AM

0 Likes
0
986
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:33 PM . Last Modified: ‎2024-03-15 03:56 AM

Darn... I really was hoping that was not the case. Has anyone experienced this before?

Thanks,
Sean

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-28 06:33 PM . Last Modified: ‎2024-03-15 03:56 AM

0 Likes
0
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-28 06:33 PM . Last Modified: ‎2024-03-15 03:56 AM

Have you tried another server of the same type, another server that you know has a PFC power supply, even another power supply in the server? If could, possibly, be the power supply not a PFC problem.

If all fails see if your friendly APC Rep will agree to swap it out for one that is compatible.

Regards
Alan G

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login