Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

PCNS3 + vMA5 + ESXi 5 Errors

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS3 + vMA5 + ESXi 5 Errors
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we?ll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5027
voidstar_apc
Janeway voidstar_apc
195
Erasmus_apc
Sisko Erasmus_apc
111
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
forced_apc
Crewman forced_apc
Crewman

Posted: ‎2021-07-01 01:07 AM

0 Likes
11
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 01:07 AM

PCNS3 + vMA5 + ESXi 5 Errors

This was originally posted on APC forums on 2/10/2012


I have installed vMA 5 on an ESXi 5 host. I installed PCNS 3 with the patch that replaced the install_en.sh and added the uninstall.

To test to make sure the machine will shut down. I use the vMA console and go to:
/opt/APC/PowerChute/group1/bin/ and run sudo ./shutdown.pl

I get:

Can't load '/usr/lib/perl5/site_perl/5.10.0/libvmatargetlib_perl.so' for module vmatargetlib_perl: libtypes.so: cannot open shared object file: No such file or directory at /usr/lib/perl5/5.10.0/x86_64-linux-thread-multi/DynaLoader.pm line 203.
at /usr/lib/perl5/site_perl/5.10.0/VMware/VmaTargetLib.pm line 10.
Compilation failed in require at /usr/lib/perl5/site_perl/5.10.0/VMware/VIFPLib.pm line 9.
BEGIN failed--compilation aborted at /usr/lib/perl5/site_perl/5.10.0/VMware/VIFPLib.pm line 9.
Compilation failed in require at ./shutdownhost.pl line 17.
BEGIN failed--compilation aborted at ./shutdownhost.pl line 17.

My next problem is I can't get to the web ui of the host, which I believe is a firewall issue and will tackle that once I know the PCNS is working.

Thanks for any help!
-Steve

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • pcns
  • vmware
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:07 AM

0 Likes
0
883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 01:07 AM

This reply was originally posted by Angela on APC forums on 1/8/2013


how to do this is in the knowledge base. search for FA159765 in http://www.apc.com/site/support/index.cfm/faq/ and refer to the section titled: How to verify communication ports are open in the vMA and how to add host servers to the server list

See Answer In Context

Reply
Replies 11
forced_apc
Crewman forced_apc
Crewman

Posted: ‎2021-07-01 01:07 AM

0 Likes
0
883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 01:07 AM

This was originally posted on APC forums on 2/10/2012


Thanks for writing, I saw that article and had replaced the files before the install.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:07 AM

0 Likes
0
883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 01:07 AM

This reply was originally posted by Angela on APC forums on 2/10/2012


i wonder if you are having this issue?

http://nam-en.apc.com/app/answers/detail/a_id/11500

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:07 AM

0 Likes
0
883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 01:07 AM

This reply was originally posted by Bill on APC forums on 2/13/2012


To verify PCNS is running run the command
sudo /etc/init.d/PowerChute status
If PCNS is running the system will return “PowerChute is running…”
If it is not running you can start it by typing
sudo /etc/init.d/PowerChute start

To test shutdown
1. CD to /opt/APC/PowerChute/group1 dir
2. run sudo bin/shutdown

Reply
forced_apc
Crewman forced_apc
Crewman

Posted: ‎2021-07-01 01:07 AM

0 Likes
0
883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 01:07 AM

This was originally posted on APC forums on 2/13/2012


Thanks for that! I got "PowerChute is running..."
Then I used the shutdown command you gave and it shutdown the host!

When I turned the host back on, I went to the logs of one of the VMs (Server 2008). It says that the previous shutdown was unexpected. Shouldn't the host shutdown the VMs first?

Reply
forced_apc
Crewman forced_apc
Crewman

Posted: ‎2021-07-01 01:07 AM

0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 01:07 AM

This was originally posted on APC forums on 2/13/2012


OK, thanks again to "i picKed a winna" and this link:
Linkie

I clicked over to this link: Linkie

And configured my automatic shutdown from there...

On my 2 Windows VMs, I altered the poweroff-vm-default.bat file and added "shutdown /s /f" to the end of the file and saved. Then when I did the "bin/shutdown" command it gracefully shutdown the VMs...

Still working on the web ui...

Message was edited by: forced

Reply
forced_apc
Crewman forced_apc
Crewman

Posted: ‎2021-07-01 01:07 AM

0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 01:07 AM

This was originally posted on APC forums on 2/13/2012


My next issue is with the web ui for the vm host. I disabled the firewall, and got a "Internet Explorer cannot display the webpage".

I added the attached apc.xml file to the /etc/vmware/firewall folder. Then I refreshed by using "esxcli network firewall refresh". When I go the security profile screen of the vm host using the vsphere client, I can see the APC id listed and it is checked. I tried the web ui again but got the same result.

the apc.xml file is:



APC

inbound
tcp
dst
3052


outbound
tcp
dst
3052


inbound
tcp
dst
6547



inbound
tcp
dst
80


outbound
tcp
dst
80


inbound
udp
dst
3052


outbound
udp
dst
3052

fale
false

Reply
boydcc_apc
boydcc_apc
Cadet

Posted: ‎2021-07-01 01:07 AM

0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 01:07 AM

This was originally posted on APC forums on 3/5/2012


force,

can you provide the details you used to fix the problem. i am having the same issues with vm's not being gracefully shutdown. I, as you, referenced the link that 'wanna' referenced.

my host shuts down but the vms hard power off.

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:07 AM

0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 01:07 AM

This reply was originally posted by Angela on APC forums on 3/6/2012


i edited the other posters post to retrieve this link for you: http://kb.vmware.com/selfservice/microsites/search.do?language=en_US&cmd=displayKC&externalId=100818...

Reply
ikram_apc
Ensign ikram_apc
Ensign

Posted: ‎2021-07-01 01:07 AM

0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 01:07 AM

This was originally posted on APC forums on 1/8/2013


Hi !

How to check or change APC FIREWALL SETTING ?

Thank you !

Reply
ikram_apc
Ensign ikram_apc
Ensign

Posted: ‎2021-07-01 01:07 AM

0 Likes
0
882
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 01:07 AM

This was originally posted on APC forums on 1/8/2013


Hi,

the link given not working, i got a same issue cannot access ui web,
maybe firewall issue.

Thank you

Reply
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 01:07 AM

0 Likes
0
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Posted: ‎2021-07-01 01:07 AM

This reply was originally posted by Angela on APC forums on 1/8/2013


how to do this is in the knowledge base. search for FA159765 in http://www.apc.com/site/support/index.cfm/faq/ and refer to the section titled: How to verify communication ports are open in the vMA and how to add host servers to the server list

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc