Ask our Experts
Didn't find what you are looking for? Ask our experts!
Share Your Feedback – Help Us Improve Search on Community! Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately. Click here to take the survey
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Free
EnglishStrengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:26 AM . Last Modified: 2024-03-11 04:07 AM
Customer with PCNS 4.2 installed on Windows.
2 x UPS groups
Group A has 2 UPS, protecting 2 x ESXi hosts in cluster with DRS Fully Automated. Pulling power on both UPS at the same time, causes "Maintenance mode" on one host which results in DRS migrating VMs to the other host. PCNS User Guide, PowerChute Network Shutdown v4.2 VMware 990-4595E-001 07/2016, p26 under "Virtual Machine Migration" states:
If you enable Virtual Machine migration, use the Duration field to set the time allowed for the VMs to migrate to another healthy Host in the Cluster. VMs will not be migrated to Hosts that are powered off, in a disconnected state, in maintenance mode, or affected by a UPS critical event.
Why is PCNS migrating VMs to the other host in the cluster that is affected by the same UPS Critical event? How do I stop this behaviour? Customer prefers to issue VMware Shutdown to hosts (rather than enter maint mode) which they advise will result in VM shutdown, not migration, under DRS Fully Automated.
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:27 AM . Last Modified: 2024-03-11 04:06 AM
Hi,
On 4/17/2018 6:11 PM, Ed said:Can you provide an update on the feature request? Has it been considered? Favourably? Any ETA?
Yes it has been considered and should be implemented in the next release. Unfortunately I do not have an ETA.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:26 AM . Last Modified: 2024-03-11 04:06 AM
Hi,
Both hosts need to be in maintenance mode to prevent the VMs from migrating. Are both hosts listed in PowerChute host protection summary as protected hosts?
On 4/15/2018 6:00 AM, Ed said:Why is PCNS migrating VMs to the other host in the cluster that is affected by the same UPS Critical event? How do I stop this behaviour? Customer prefers to issue VMware Shutdown to hosts (rather than enter maint mode) which they advise will result in VM shutdown, not migration, under DRS Fully Automated.
We are looking to add the option of not putting the host into maintenance mode and adding that feature to a future release.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:26 AM . Last Modified: 2024-03-11 04:06 AM
Thanks for the reply Bill
Yes, both hosts are listed as protected and the cluster consists of only those 2 hosts.
Can you provide an update on the feature request? Has it been considered? Favourably? Any ETA?
Looking through this forum it appears there are a lot of us (desperately) wanting this feature.
Thanks for you ongoing and prompt responses
Ed
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:27 AM . Last Modified: 2024-03-11 04:06 AM
Hi,
On 4/17/2018 6:11 PM, Ed said:Can you provide an update on the feature request? Has it been considered? Favourably? Any ETA?
Yes it has been considered and should be implemented in the next release. Unfortunately I do not have an ETA.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.