PowerChute with Macs

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute with Macs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:25 AM . Last Modified: ‎2024-03-11 04:07 AM

0 Likes
8
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:25 AM . Last Modified: ‎2024-03-11 04:07 AM

PowerChute with Macs

I've installed PowerChute on a couple Mac Pros, one running OS 10.12 and the other 10.11. I still need to do the configuration however and am having trouble. Can the configuration only be done by accessing the machines over the network (not locally)?

I'm having trouble accessing the machines over the network. I add TCP port 6547 to the end of the IP address but no luck.

Anyone know the procedure for a Mac?

Thanks a lot.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

Hi Bill,

Looks like JDK 8.171 is the overall winner.

I had trouble when I was using JDK 9.0.4 on OS 10.12.6. It hung as you describe.

It would be helpful if APC update the installation guide as it does say that Java version 8 or greater should be installed on Macs.

Thanks again.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:25 AM . Last Modified: ‎2024-03-11 04:07 AM

0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:25 AM . Last Modified: ‎2024-03-11 04:07 AM

Hi,

Open web browser on the Mac and enter https://system ip:6547 Example https://192.168.1.10:6547. If you do not want to configure using the web interface you can stop the PowerChute service and edit pcnsconfig.ini that will be found in the folder PowerChute was installed to. The default install path is /Users/Shared/Applications/APC/PowerChute Then restart the service.

See Schneider Electric FAQ FA159757 for assistance with the ini file. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

Thanks, Bill. The directions were spot on and I had no trouble configuring one of the Macs. I had been using http instead of https- that was the problem.

Unfortunately I can't get the other Mac to register. It seems to get stuck at this stage: "Please wait while PowerChute registers with the Network Management Card(s). This may take a few minutes." There is no error message.

I've enabled Java in the browser and also pop ups are allowed. Any other ideas?

Thanks for your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

Hi,

Does the software hang at the point of registering or does ot fail with no error message? If it fails with no error and you proceed what is reported in the error.log file. The error log will be found in the PowerChute install directory. Another thing to check is to see if the computers IP address is being added to the PowerChute client list on the NMC.

The 2 main reasons for failure to register are

1 - Mismatched subnet mask between he NMC and computer.

2 - Blocked port. PCNS will contact the NMC via http port 80 or https 443 and once communication has been established the NMC communicates with PCNS on UDP port 3052

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

It hangs at the point of registering. I'm able to enter all the credentials okay but it just doesn't register. Here is the error message from the log:

03-05-18 03:16:14,452 ERROR pool-2-thread-22 com.apcc.m11.components.WebServer.CfgWizard.SessionManager - applySettings Exception
java.lang.NullPointerException

I'm using Java 9.0.4 on the machine that won't register. On the machine that did register Java 8 update 161 is being used. By chance should I go back a version of Java? The machine having trouble is running OS 10.12.6.

The subnet mask looks fine and the ports appear to be open. The Mac's IP is listed in NMC. I did that in advance.

I greatly appreciate your help.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

Do you think the Java version could be the problem? Thanks.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

Hi,

It could be the Java. PCNS 4.2 was tested on OSX 10.3.3 with JDK version 8.162. I have installed on OSX 10.3.4 with JDK 8.171 with no issues. I also installed JDK 10.0.1 on High Sierra and PCNS installed but hung during the NMC connection phase. I was not able to test JDK 9.0.4 as Oracle removed it from their site. 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

Okay, so I found a solution for the second Mac. I uninstalled the 9.0 JDK (using Terminal and not easy to do because directions were not clear) and installed Java 8 Update 171. Then I installed PowerChute 4.1. This combo registered without a problem. I used the older PowerChute version because that's what I installed on the other Mac that had successfully registered.

Perhaps I had a bad install of Java 9.0 but it's also possible that this version of Java isn't always compatible with a particular OS and version of PowerChute.

Btw, the JDK (not just the JRE) must be installed on Macs according to APC instructions for PowerChute version 4.2:

Note: For Mac OS® X, JDK 8 or greater must be installed as the JRE does not contain the required files to run PowerChute.

Installing on Macs was certainly not as easy as Windows.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

0 Likes
0
1283
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 12:26 AM . Last Modified: ‎2024-03-11 04:07 AM

Hi Bill,

Looks like JDK 8.171 is the overall winner.

I had trouble when I was using JDK 9.0.4 on OS 10.12.6. It hung as you describe.

It would be helpful if APC update the installation guide as it does say that Java version 8 or greater should be installed on Macs.

Thanks again.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore