Hi all. Can someone tell me how to reset my Powerchute software install to its initial settings (time to shutdown, etc.)? I have my login credentials...I imagine it's a fairly simple process. Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:27 AM . Last Modified: 2024-03-11 04:06 AM
Hi,
Sorry but there is not a reset to defaults button. The default power outage settings are, at runtime limit 120 seconds, Time for operating system to shut down 180 seconds. You can run the initial setup wizard by clicking on the Shutdown tab on the main menu and select Initial Setup.
If you need to reset you can uninstall and reinstall.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:27 AM . Last Modified: 2024-03-11 04:06 AM
Hi,
Are you running PowerChute Business Edition or PowerChute Network Shutdown and what version number?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:27 AM . Last Modified: 2024-03-11 04:06 AM
Business edition 9.5. Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:27 AM . Last Modified: 2024-03-11 04:06 AM
Hi,
Sorry but there is not a reset to defaults button. The default power outage settings are, at runtime limit 120 seconds, Time for operating system to shut down 180 seconds. You can run the initial setup wizard by clicking on the Shutdown tab on the main menu and select Initial Setup.
If you need to reset you can uninstall and reinstall.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 12:27 AM . Last Modified: 2024-03-11 04:06 AM
That answers it. Thanks!