PCNS 2.2.4 on ESX 4.0 shutdown assistance

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PCNS 2.2.4 on ESX 4.0 shutdown assistance
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Erasmus_apc
Sisko Erasmus_apc
112
TheNotoriousKMP_apc
Sisko TheNotoriousKMP_apc
108
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:34 PM . Last Modified: ‎2024-02-14 11:47 PM

0 Likes
3
780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:34 PM . Last Modified: ‎2024-02-14 11:47 PM

PCNS 2.2.4 on ESX 4.0 shutdown assistance

We have an APC Smart-Ups 1500 attached to an HP DL360 G7 Server running ESX4.0. I need assistance configuring the NMC to shutdown the two guest OSes and then ESX host afte running on battery for 15 minutes and then automatically powering back up after power has been restored. I have both Power cords to server plugged in to the Main Outlet Group on the APC. I have installed and configured PCNS 2.2.4 successfully. Here is some information on our setup:


APC SMT1500 (Smart-Ups 1500) SN# AS1046122131 (Firmware ID17UPS 05.0)
NMC 9631 w/Environment Sensor

HP Proliant DL360 G7
OS - ESX 4.0

Two Guests running Win2003 STD SP2


APC NMC - 192.168.1.10
ESX - 192.168.1.15
Guest 1 - 192.168.1.20
Guest 2 - 192.168.1.21

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:34 PM . Last Modified: ‎2024-02-14 11:47 PM

0 Likes
0
779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:34 PM . Last Modified: ‎2024-02-14 11:47 PM

all of that sort of happens automatically. take a look at this document -> http://www.apcmedia.com/salestools/TDOY-5UQVBV_R2_EN.pdf

it discusses how the NMC and PCNS talk to each other over the network. you may want to login to PCNS as described in the earlier documents i provided to configure your ESX's PCNS installation to shutdown after the UPS has been on battery after the 15 minutes part of your setup.

booting back up after utility power is restored to the UPS is the default setting. as long as the BIOS of the host ESX box is set to "last state" or "always on," it should back on automatically once the UPS wakes up from sleep mode, which is what it goes into when it discharges its battery and waits for utility power.

all of the settings in the NMC that you need to review are on the UPS tab-> Configuration-> Shutdown section of the NMC. the "low battery duration" is the amount of runtime remaining when the UPS will signal everything attached that it is going to shutdown in X minutes. the default is generally 2 minutes on most UPS models. if you install PCNS and don't do any special configuration, your PCNS clients will shutdown when the UPS hits this low battery duration. thus, you should just need to login to your ESX PCNS configuration as I mentioned and configure the UPS On battery event to shutdown the system after the event lasts for 15 minutes. once that happens, then you follow that document that tells you how to have ESX shut down your guests.

let me know if you need more help..

P.S. - I guess the other option I forgot to mention, since your ESX guests are bridged to the same network as ESX, is just installing the regular free version of windows PCNS on those and have those operate on the network and talk to PCNS and shutdown when you want them to. it may be safer to do it by having ESX shut them down though just incase ESX shuts down first for some reason..

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:34 PM . Last Modified: ‎2024-02-14 11:47 PM

0 Likes
0
779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:34 PM . Last Modified: ‎2024-02-14 11:47 PM

these articles should help you get started:

1.) installing -> http://nam-en.apc.com/app/answers/detail/a_id/10330 or http://nam-en.apc.com/app/answers/detail/a_id/9920

2.) configuring -> http://nam-en.apc.com/app/answers/detail/a_id/10380

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:34 PM . Last Modified: ‎2024-02-14 11:47 PM

0 Likes
0
779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:34 PM . Last Modified: ‎2024-02-14 11:47 PM

Thanks for the links...all have been followed exactly. I am more in need of how to actually configure the NMC to send the shutdown command to ESX after being on battery for 15minutes allowing enough time to gracefully shutdown both guests and ESX, then boot back up after power has been restored. I have the NMC 2.0 User Guide, but there are many very confusing/conflicting statements and we have spent weeks trying to make this work correctly.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 11:34 PM . Last Modified: ‎2024-02-14 11:47 PM

0 Likes
0
780
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 11:34 PM . Last Modified: ‎2024-02-14 11:47 PM

all of that sort of happens automatically. take a look at this document -> http://www.apcmedia.com/salestools/TDOY-5UQVBV_R2_EN.pdf

it discusses how the NMC and PCNS talk to each other over the network. you may want to login to PCNS as described in the earlier documents i provided to configure your ESX's PCNS installation to shutdown after the UPS has been on battery after the 15 minutes part of your setup.

booting back up after utility power is restored to the UPS is the default setting. as long as the BIOS of the host ESX box is set to "last state" or "always on," it should back on automatically once the UPS wakes up from sleep mode, which is what it goes into when it discharges its battery and waits for utility power.

all of the settings in the NMC that you need to review are on the UPS tab-> Configuration-> Shutdown section of the NMC. the "low battery duration" is the amount of runtime remaining when the UPS will signal everything attached that it is going to shutdown in X minutes. the default is generally 2 minutes on most UPS models. if you install PCNS and don't do any special configuration, your PCNS clients will shutdown when the UPS hits this low battery duration. thus, you should just need to login to your ESX PCNS configuration as I mentioned and configure the UPS On battery event to shutdown the system after the event lasts for 15 minutes. once that happens, then you follow that document that tells you how to have ESX shut down your guests.

let me know if you need more help..

P.S. - I guess the other option I forgot to mention, since your ESX guests are bridged to the same network as ESX, is just installing the regular free version of windows PCNS on those and have those operate on the network and talk to PCNS and shutdown when you want them to. it may be safer to do it by having ESX shut them down though just incase ESX shuts down first for some reason..

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of