Enabling SNMP v1 on an NMC installed on a Smart-UPS RT 10000 XL
  • Enabling SNMP v1 on an NMC installed on a Smart-UPS RT 10000 XL
Posted: ‎2021-07-08 11:34 PM . Last Modified: ‎2024-02-14 11:47 PM
4602
I enabled SNMP on the NMC, but cannot get/walk using a SNMP command line client
Seems that SNMP is not enabled since a nmap scan does not show the 161 UDP port open.
Checked everything : community names, IP configuration, gateways, masks. The client and the NMC are on the same subnet.
I wonder if you have to reboot the UPS to enable SNMP.
And if so, will it shutdown power to the loads during the reboot ?
Thanks for any info.
problem solved.
To activate SNMP v1 it was necessary to reboot the NMC
Thank you for the solution
Hi RodV, you can reboot the NMC (admin -> general -> reset/reboot -> reboot management interface) without having it effect your load (the NMC and the UPS are separate in that fact) however rebooting the ups will take your load down. As for the actually troubleshooting, i would also check to make sure you have the latest powernet MIB installed as well as open ports 161 and 162 UDP. I see you checked the community names, how baout the access type for the community name/s as well. Hope this helps.
it may be helpful for you to post your config.ini file for us as well, using these instructions -> http://nam-en.apc.com/app/answers/detail/a_id/9321
also, are you using SNMPv1 or SNMPv3? what CLI utility are you using? can you tell us what syntax you are using?
problem solved.