Older AP9630 NMC2 card won't fit into Smart UPS 2200
  • Older AP9630 NMC2 card won't fit into Smart UPS 2200
Posted: ‎2021-06-29 01:32 AM . Last Modified: ‎2024-03-13 05:26 AM
2102
What is the difference between the older AP9630 NMC2 cards with a shorter vertical slot/opening on the right-hand side of the card's front panel, and the newer AP9630 NMC2 cards with a taller slot?  Just replaced an older Smart UPS 2200 (SUA2200RM2U) with a newer Smart UPS 2200 (SMT2200RM2U), and mistakenly assumed that the old AP9630 NMC2 could be re-used.  It did not fit because there is a taller tab that requires the taller slot/opening to accommodate it.
What is the difference - I thought any AP9630 NMC2 would be sufficient.
AP9630 NMC2
As suggested, I called tech support and they happily sent me a replacement faceplate.
Replies 4
Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander
There was a run of those cards that incorrectly had the smaller tab. I forget the serial number range, but I think it was from 2009. I think if you call tech support with the card's serial number, they can send you a replacement faceplate. If not, post a reply and one of the APC folks here can probably get it to you.
Robert,
Contact Technical Support at 1-800-890-4272 and they will send you out a replacement cover that has the proper size slots.
Yeah, I just had the same problem, faceplate with APC (not Schneider) and short slot on RHS.  PCB REV05 Copyright 2008.
I wanted to put the 9630 in an SMT1000, but it won't go.
So thanks for the info, I'll get the hacksaw out now....
  • 9630
  • ap
  • smartslot