NMC AP9635 Modbus RS485 Issue In Galaxy 5000

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • NMC AP9635 Modbus RS485 Issue In Galaxy 5000
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

1 Like
11
3411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

NMC AP9635 Modbus RS485 Issue In Galaxy 5000

HI,

I have been trying to connect with Galaxy 5000 using NMC AP9635 trough RS485.I am looking for support on following:

  1. Is Modbus RS485 Is default enabled ?? If not Then How to Enable and do the parameter setting.
  2. What are default connection Type (2 Wire or 4 Wire) 
  3. What are the default parameters for RS-485 ( Device Address, Baud Rate, Parity etc).
  4. What Minimun NMC Firmware required for Modbus

Furhter i have tried to access the modbus setting through webpage but it is just showing Modbus TCP option.(Snap Attached)

Currently NMC have V 5.2.1 Firmware (Snap attached)

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:16 AM

1 Like
0
3411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:16 AM

Hi Angela,

We are already in contact with "SELVAKUMARAN NAMBIRAJAN" from APC and following the attached document shared by them.

and YES i am trying to access the 66061 directly from RS485 port.

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

0 Likes
0
3411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

Angela 

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

0 Likes
0
3411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

As far as I can tell, only Modbus TCP is currently supported for this UPS and 'chu' application as per the register map:

http://www.apc.com/salestools/LARD-9K3GSQ/LARD-9K3GSQ_R0_EN.pdf 

I will see if Modbus serial is planned for a future firmware release or if we can log it as an enhancement request.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

0 Likes
0
3411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

I am finding that the current solution for Modbus RS-485/serial on this UPS is to use a MGE BMS card 66061 in the multi-slot.

To clarify, if you are using AP9635 you would likely already have a 66061 connected to your AP9635 as part of the kit AP9635 for G5K - part number G5K9635CH, but you would need an additional 66061 to provide Modbus serial or else AP9635 will not show any data. (66061 card is how the AP9635 receives data from the UPS and cannot be disconnected without loss of data in AP9635.)

This requires some setup to get working so you'd need to contact your local service team for more detailed support and help getting this set up and configured.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

0 Likes
0
3411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

Angela are you saying that i need to use following to enable Galaxy 5000 over RS-485:

1 No. of  AP9635 Card

1 No. of G5K9635CH Card

2 Nos. of  66061 Cards

Please confirm

BR

Genjua

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

0 Likes
0
3411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

Hi,

Only 66061 is required for RS-485 specifically.

AP9635 supports Modbus TCP only and you already seem to have that. I mentioned some of the other things since it seems you have an AP9635 already installed in this UPS and did not want you to be confused that AP9635 requires its own dedicated 66061 card as part of installation. Dedicated/second 66061 is required for Modbus serial/RS-485.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

0 Likes
0
3411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

Hi Angela,

Yes there is 66061 card available on UPS and i have tried to fetch the RS485 data directly from it using this FAQ.

http://www.apc.com/us/en/faqs/FA354828

But still unable to even get connection with device by using the procedure mentioned in above FAQ.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

0 Likes
0
3411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

Good Day Angela,

Mr. Usman is my college he is currently on the site and trying to communicate the UPS on Modbus RTU.

With Reference to http://www.apc.com/salestools/LFLG-A32FWS/LFLG-A32FWS_R1_EN.pdf note# 2 is saying "Modbus Serial RTU is supported on NMC model AP9635, and Modbus TCP is supported on NMC models AP9635, AP9630, AP9631 and AP9537SUM."

which means modbus RTU and Modbus TCP both are supported.

Please Advise/Comment.

BR

Genjua

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

0 Likes
0
3411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

Hi Genjua,

That URL you sent is the register map is for MGE Galaxy 3500 and Smart-UPS VT as well as single phase Smart-UPS where yes, AP9635 (and other NMC models) does both RTU and Modbus TCP within its firmware application.

The statement at the top "MGE Galaxy" is generic so I can see where it is confusing. I will ask that it get updated to specify MGE Galaxy 3500 which is a totally different UPS/design.

Based on Galaxy 5000 UPS design, it is not possible to do Modbus serial/RTU direct from AP9635 unfortunately. It has to be done by 66061 in the multi-slot.

If you look at the AP9635 you have today, it's Modbus RTU is likely connected to a dedicated 66061 installed at the same time AP9635 was. If you disconnect this, then AP9635 won't work because the Modbus connection from 66061 is how it "talks" to the UPS. A second, dedicated 66061 must be added to get Modbus serial/RS-485. I suppose if you don't want to use AP9635 anymore, you could just use the single 66061 you have too.

I am not familiar with setting this up so if you think you have what's required and have it set up properly, I suggest to contact 3ph support in your region to get some guidance.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

0 Likes
0
3411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:17 AM

Angela thanks much for your comment, we will check UPS by adding 2nd 66061 card.

One more thing i want to discuss in current scenario if we disconnect 66061 with AP9635 and connect it with laptop using RS-485 converter, we do not get any data on modbus it says device not connect.  Why is this happening?

Please comment/advise.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:16 AM

0 Likes
0
3411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:16 AM

Hi Genjua,

I'm not sure to be honest. I did hear from a colleague that there are a few jumpers on the 66061 that need to be set a certain way when using AP9635. I am not sure if they need to be changed if you're not using it with AP9635 but rather a PC or BMS. Baud rate is also set to 1200 when used with AP9635, is that what Mr. Usman was trying when connected to a PC?

Did you want me to try to get a local support expert to contact you and Mr. Usman on this directly?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:16 AM

1 Like
0
3412
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-08 05:29 AM . Last Modified: ‎2024-02-15 12:16 AM

Hi Angela,

We are already in contact with "SELVAKUMARAN NAMBIRAJAN" from APC and following the attached document shared by them.

and YES i am trying to access the 66061 directly from RS485 port.

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore