Matrix with AP9606 - Error - UPS Not Supported by this application

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Matrix with AP9606 - Error - UPS Not Supported by this application
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
MarkGinger_apc
Lieutenant MarkGinger_apc
Lieutenant

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:18 AM

0 Likes
5
1199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:18 AM

Matrix with AP9606 - Error - UPS Not Supported by this application

We've replaced our Matrix 5000 (original died) and moved our AP9606 to the new Matrix. When we try to access the Matrix through the SNMP Interface we get an error "A UPS was found that is not supported by this application. Check the CD-ROM for the correct APP or contact technical support". The original Matrix's firmware was 5Z1, replacement Matrix is 3Z. Does anyone know what the issue might be? Does the firmware on the AP9606 need to be updaded? Last update was 2008. Does the Matrix need a firmware update? Thanks for any help!

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
0
1199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:17 AM

Ok, that should be fine. I'd reseat the EU then as a start if you can.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
0
1199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:17 AM

On your AP9606, under Help->About system, can you let me know what you see for AOS and app versions? The letter Z in the firmware is supposed to indicate the Matrix supports this accessory.

Can you verify you did not connect any serial cable to the Matrix? Another thing we may want to do is reseat the EU now that the AP9606 is installed assuming no serial cable was connected.

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkGinger_apc
Lieutenant MarkGinger_apc
Lieutenant

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
0
1199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:17 AM

AOS v3.2.5

App v3.2.6

There are no cables connected to the Matrix.

We have not done an EU reseat yet.

Should we go ahead with the reseat?

Is there any firmware changes that may be required?

Thanks for your help!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
0
1199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:17 AM

Hi again,

What is the app name - do you see it sy or sumx for the module name? If I know that, I can tell if there is potentially an issue with the NMC firmware. I don't think there is anything wrong with the Matrix firmware since it is still Z and plus it cannot be modified anyway.

I'd go ahead with the EU reseat only after we confirm the module name for the APP you referenced to avoid wasting time with that.

Reply

Link copied. Please paste this link to share this article on your social media post.

MarkGinger_apc
Lieutenant MarkGinger_apc
Lieutenant

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
0
1199
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:17 AM

App name: sumx326.bin

AOS  aos325.bin

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:17 AM

0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 08:07 AM . Last Modified: ‎2024-03-12 03:17 AM

Ok, that should be fine. I'd reseat the EU then as a start if you can.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore