Dear All,
I have a challenge with MGE Galaxy 5000 60KVA UPS I recently installed. when I powered the UPS and it goes through initializing process, this error code appears on the screen" External Communication error 7-5-1" and the UPS will not start.
The UPS came with External Battery Circuit Breaker Cabinet (MGE Galaxy 6000)
What could be the the possible cause?
Please help
Best Regards,
Oppong
Message was edited by: oppong03
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:43 AM . Last Modified: 2024-03-19 12:37 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:43 AM . Last Modified: 2024-03-19 12:37 AM
dear oppong
checked u ups parallel or signal ups ? i think u have a parallel ups , u connect the xms07 parallel connector red
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:43 AM . Last Modified: 2024-03-19 12:36 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:43 AM . Last Modified: 2024-03-19 12:37 AM
Dear All,
I have a challenge with MGE Galaxy 5000 60KVA UPS I recently installed. when I powered the UPS and it goes through initializing process, this error code appears on the screen" External Communication error 7-5-1" and the UPS will not start.
The UPS came with External Battery Circuit Breaker Cabinet (MGE Galaxy 6000)
What could be the the possible cause?
Please help
Best Regards,
Oppong
Message was edited by: oppong03
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:43 AM . Last Modified: 2024-03-19 12:37 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:43 AM . Last Modified: 2024-03-19 12:37 AM
dear oppong
checked u ups parallel or signal ups ? i think u have a parallel ups , u connect the xms07 parallel connector red
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:43 AM . Last Modified: 2024-03-19 12:37 AM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:43 AM . Last Modified: 2024-03-19 12:37 AM
Hello Oppong,
I think you need to send a personalisation file by using the "software tuner". If you haven't, try to contact one of APC authorized service partners.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:43 AM . Last Modified: 2024-03-19 12:36 AM
I seem to have a problem of identification of the UPS because if you have a solution in parallel must have a different name, this configuration is the software makes communication.
you can write me to this email to have contact and sharing newsletters failures and solutions in the galaxy
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-26 05:43 AM . Last Modified: 2024-03-19 12:36 AM
jdorado@outlook.com
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.