How to change SRT192RMBP2 Battery Pack number

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase โ†’ Use quotes " " (e.g., "error 404")
  • Wildcard โ†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR โ†’ Combine keywords (e.g., login AND error, login OR signโ€‘in)
  • Keep it short โ†’ Use 2โ€“3 relevant words , not full sentences
  • Filters โ†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • How to change SRT192RMBP2 Battery Pack number
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
darxis
darxis
Cadet

Posted: โ€Ž2024-12-19 10:32 AM

0 Likes
3
982
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2024-12-19 10:32 AM

How to change SRT192RMBP2 Battery Pack number

I have acquired a used SRT8KRMXLI (ID1014) with one SRT192RMBP2 battery pack.

After installing the units I can see that the battery pack is incorrectly detected as "Battery Pack 2" I have only one SRT192RMBP2 unit connected. The UPS should detect it as "Battery Pack 1" as it is the only one connected.

 

I guess it is probably because the previous owner had another copy of a SRT192RMBP2 battery pack connected to the UPS in the past (with a different S/N) and the UPS remembered that and it is reserving the "Battery Pack 1" "slot" for the previously connected SRT192RMBP2.

Please see the attached screenshot below.

 

I would like to make the installed SRT192RMBP2 battery pack as "Battery Pack 1".

 

What I have tried and didn't work:

- upgraded the UPS firmware to the latest UPS 15.2 (ID1014) firmware using serial connection with the battery pack disconnected

- upgraded the UPS firmware to the latest UPS 15.2 (ID1014) firmware using serial connection with the battery pack connected

- upgraded the built-in NMC2 firmware

- upgraded the add-on NMC2 firmware

 

Please help me setting my single battery pack as "Battery Pack 1" instead of "Battery Pack 2". Is there any way to tell the UPS to forget the previously installed BP (assuming that the problem is that it still remembers it)?

BP.png

 

Labels
  • Labels:
  • Smart-UPS & Symmetra LX-RM
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Teken
Kirk Teken
Kirk

Posted: โ€Ž2024-12-20 03:50 AM . Last Modified: โ€Ž2024-12-20 03:52 AM

0 Likes
2
959
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2024-12-20 03:50 AM . Last Modified: โ€Ž2024-12-20 03:52 AM

First thing is to remove the extra NMC. Disconnect the external battery pack from the main system.


Hard boot the system with both battery cartridges removed and AC Mains disconnected.

 

Wait about 10-15 seconds while pressing the power button. Restore AC Mains and power up the system without the battery cartridges installed.

 

Wait for the system to declare a battery fault and wait another 10-15 seconds. Login to the internal NMC and verify there is no external battery pack installed.

 

If no external battery pack is seen and detected reconnect (only) the main battery cartridge for the system. The system should prompt you to confirm if this is a new battery cartridge so toggle from No to Yes.

 

Enter the current month and year and hit save. Go back to the internal NMC and verify the new battery installation date is present.

 

If yes proceed to connect the external battery pack (without) the cartridges. Watch the front of the external battery pack LED. It should begin to flash and if there is a pending firmware update the main system will update the same. 

If there is an error as it relates to a firmware error you must update the firmware again (with) the external battery pack attached.

 

Verify the external battery pack is seen and report back what it says. If itโ€™s present insert a single battery cartridge into the unit and wait for the system to prompt you to enter the battery installation date.

 

Repeat the same for the second cartridge and hit save. Turn the output back on and wait for the system to complete the internal self test.

 

If no self test is done manually initiate the self test and wait for it to complete. Go back to the internal NMC.

 

What does the system indicate as the external battery pack?!?

Reply

Link copied. Please paste this link to share this article on your social media post.

darxis
darxis
Cadet

Posted: โ€Ž2024-12-22 03:43 PM

In response to Teken
0 Likes
1
900
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2024-12-22 03:43 PM

Hi Teken, thanks for your reply.

I followed exactly step by step what you've written but it didn't work. As soon as I reconnected the external BP in your instructions the BP was identified as "Battery Pack 2" again on the UPS LCD and in the internal NMC. Please see the photo of the UPS LCD after I reconnected the external BP with the 4-pin blue cable.

 

IMG_20241222_233725.jpg

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Teken
Kirk Teken
Kirk

Posted: โ€Ž2024-12-26 09:29 AM

In response to darxis
0 Likes
0
860
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2024-12-26 09:29 AM

Hi,

 

I had the chance to test a similar unit and the system does acknowledge the battery pack of 1 / 2. I would suggest you try the brain dead procedure 2-3 times with the external battery pack connected / disconnected:

 

https://www.apc.com/us/en/faqs/FA156611/

 

As reluctant as I am to suggest the following a UPS firmware load with both units connected may resolve this issue. Regardless, I would submit a service request with APC Technical Support to see if they can offer other alternatives.

 

Let me know how it all ends up good or bad. ๐Ÿ‘

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 

Youโ€™ve reached the end of your document

WHATโ€™S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore