Firmware Update from V6.2.1 to V6.4.0 not working (FTP Error)

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Firmware Update from V6.2.1 to V6.4.0 not working (FTP Error)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 03:58 AM . Last Modified: ‎2024-03-13 01:58 AM

0 Likes
3
2370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:58 AM . Last Modified: ‎2024-03-13 01:58 AM

Firmware Update from V6.2.1 to V6.4.0 not working (FTP Error)

Hello,

I want to update the Firmware in my AP9631 NMC2 card, that is installed into a
SmartUPS RT 3000 XLI System.

Actual running is the Firmware V6.2.1 without problems.
I download the new Firmware V6.4.0.
Then I allow Telnet, FTP and http, delete the old SSH key and also the old SSL key.
Starting with the application FW_Upgrade_R2.exe.
The begin of the upgrade process looks good. Ping is OK and I select Upgrade Now.
Testing FTP Log-in is passed.
The process begin to transfer the firmware file (1/3): Boot Monitor
Boot Monitor transfer successful
Restarting network interface
Device connection passed
Testing FTP Log-In
ERROR FTP Log-in failed.

Why that? The upgrade process stops.
I can login via telnet to the NMC2 but I can't login via http. The GUI does not start.

Can you help me please?

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ftperror
  • upgrade
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:58 AM . Last Modified: ‎2024-03-13 01:58 AM

0 Likes
0
2370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:58 AM . Last Modified: ‎2024-03-13 01:58 AM

Glad it worked and you're all set! Thanks for the positive feedback. Yes, that new version of firmware I also like because it gives our customers a lot of security enhancements and javascript menus that stay open when you click on them laughing

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 3
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:58 AM . Last Modified: ‎2024-03-13 01:58 AM

0 Likes
0
2370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:58 AM . Last Modified: ‎2024-03-13 01:58 AM

I suggest trying a manual upgrade through FTP as described here for NMC2 -> http://www.schneider-electric.us/en/faqs/FA156047 

You can start with just the AOS (APC OS) and then the application file (you don't need to do bootmonitor module twice since it already seems like it went). This could've been caused by a timing/network issue where the upgrade tool couldn't log in via FTP because perhaps the NMC wasn't fully booted or something. You can also retry the tool or just jump to manual FTP method which is what I recommend and is outlined in the article above with the detailed steps including when a reboot is needed.

The GUI doesn't work since your application .bin file is likely missing which contains all of the web pages.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 03:58 AM . Last Modified: ‎2024-03-13 01:58 AM

0 Likes
0
2370
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:58 AM . Last Modified: ‎2024-03-13 01:58 AM

Hello Angela,

thanks for your help. Yes, I already found this documentation on your webpage regarding the manual update process.
But before I start this I tried to do the complete update process with the tool via an other workstation and
this is fully working. I'm very happy and the new application looks great.
After Upgrade I can login again via the GUI and I can create a valid certificate for Web access via https and
also I can create a valid host key for SSH connection.
Its all working and again Thank you very much!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 03:58 AM . Last Modified: ‎2024-03-13 01:58 AM

0 Likes
0
2371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 03:58 AM . Last Modified: ‎2024-03-13 01:58 AM

Glad it worked and you're all set! Thanks for the positive feedback. Yes, that new version of firmware I also like because it gives our customers a lot of security enhancements and javascript menus that stay open when you click on them laughing

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore