Email Notification keep sending non-stop

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Email Notification keep sending non-stop
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:08 AM . Last Modified: ‎2024-03-13 01:04 AM

0 Likes
2
4362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:08 AM . Last Modified: ‎2024-03-13 01:04 AM

Email Notification keep sending non-stop

When we encountered a power failure over the weekend, we keep receiving the alert notification every 2 min non-stop. This did not stop despite I log in to reconfigure it to repeat only 3 times. Thus, I was forced to disable the notification altogether. Is the non-functional repeat option a known bug?

If I am to increase the repeat of the same alert to 2 hours instead of 2 min, I assume the first alert will still be sent immediately instead of 2 hours later right?

For the convenient of major users, is it possible to configure the default setting to repeat only 3 times for the same alert for all notifications? If not, it will be really troubleshoot to do this on every single type of notification one-by-one, not to mention the frustration of receiving it every 2 min for every type of notification.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-06-29 05:08 AM . Last Modified: ‎2024-03-13 01:04 AM

0 Likes
0
4361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:08 AM . Last Modified: ‎2024-03-13 01:04 AM

I believe you have a network management card (AP967/1/9 or AP9630/1) which is sending these. You can view them in the web interface under Administration / Notification / Event Actions / by event and then selecting the particular event you're interested in and then clicking on the individual event. You can control initial delay / repeat / repeat interval / duration (max of N messages or until cleared) per recipient.

When I make bulk changes to these, I FTP to the unit, get the config.ini file, do a global find/replace in notepad in the EventActionConfig section, then FTP the file back. You probably want to set one of these via the web interface to see what the desired string is - the config.ini version is rather cryptic.

Note: Unless you disable or rate-limit it, when you put the config.ini file back you'll get one notification email for each parameter you changed while editing.

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-29 05:08 AM . Last Modified: ‎2024-03-13 01:04 AM

0 Likes
0
4361
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:08 AM . Last Modified: ‎2024-03-13 01:04 AM

May I know what software or hardware are you using to send an e-mail notification?

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-29 05:08 AM . Last Modified: ‎2024-03-13 01:04 AM

0 Likes
0
4362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 05:08 AM . Last Modified: ‎2024-03-13 01:04 AM

I believe you have a network management card (AP967/1/9 or AP9630/1) which is sending these. You can view them in the web interface under Administration / Notification / Event Actions / by event and then selecting the particular event you're interested in and then clicking on the individual event. You can control initial delay / repeat / repeat interval / duration (max of N messages or until cleared) per recipient.

When I make bulk changes to these, I FTP to the unit, get the config.ini file, do a global find/replace in notepad in the EventActionConfig section, then FTP the file back. You probably want to set one of these via the web interface to see what the desired string is - the config.ini version is rather cryptic.

Note: Unless you disable or rate-limit it, when you put the config.ini file back you'll get one notification email for each parameter you changed while editing.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.