Cannot login to NMC using APC InfraStruxure Manager

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • Cannot login to NMC using APC InfraStruxure Manager
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:16 PM

0 Likes
5
1328
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:16 PM

Cannot login to NMC using APC InfraStruxure Manager

I am having trouble logging into some of our APC UPS via the APC InfraStruxure Manager.

If the UPS is set for HTTP login, the APC Manager can login to all UPS just fine. However, we would like to use HTTPS. When using HTTPS, we are able to login to some using the Manager, but not others. Strangely, the ones that I cannot login to via HTTPS in the Manager don't work using IE8 either. I get this message, "Internet Explorer cannot display the webpage". But if I try to HTTPS into them using FireFox, it works fine. I have tried resetting my IE8 settings, didn't make any difference. The Infrastruxure Manager doesn't working using FireFox, so that doesn't do me much good.

I have not checked all of them, but it seems so far that our newer UPS(with newer style NMC) can be logged into via the Manager using HTTPS without issue, but the older UPS/NMC cannot be logged into with HTTPS from the Manager.

I see this error upon launching the Manager via IE8. I'm not sure if it's related at all. "APC InfraStruxure Manager LSP install failed with win32 error code 1603."

I am unsure if we have the newest version of the Manager, we have version 4.7 Build 275. Model number of the Manager is AP92200, Hardware Revision 1.0, Mfg Date 6/1/2006.

When I try to check for Updates from the Manager, it says "Error checking for updates".

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:16 PM

0 Likes
0
1329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:16 PM

Your issue with IE8 and HTTPS on AP9617/18/19 is most likely this -> www.apc.com/site/support/index.cfm/faq/ -> search for FA162031

Also, 4.7 is the newest build of manager but it has been discontinued for some time and also prior to IE8 release. Thus, I don't think we can support IE8 and ISX manager if it does not work. Anyway, I don't think that matters because of the issue I believe you're having is related to a windows update blocking 768 bit certs.

Since ISX Manager is so old, I am not sure if there is a way to check for updates any more unfortunately.

Anyway, if you read up on the knowledge base I linked you to, that will explain the HTTPS issue with the older cards. If IE8 works fine for ISX manager beyond that, then keep using that and figure out the best way for you to address the HTTPS issue. Let me know if you have any questions. After reading the article, let me know what you think. If you have many cards, I might have an option I can provide to you to automate the 1024 bit cert creation (which after you read FA162031 should make sense).

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:16 PM

0 Likes
0
1330
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:16 PM

Your issue with IE8 and HTTPS on AP9617/18/19 is most likely this -> www.apc.com/site/support/index.cfm/faq/ -> search for FA162031

Also, 4.7 is the newest build of manager but it has been discontinued for some time and also prior to IE8 release. Thus, I don't think we can support IE8 and ISX manager if it does not work. Anyway, I don't think that matters because of the issue I believe you're having is related to a windows update blocking 768 bit certs.

Since ISX Manager is so old, I am not sure if there is a way to check for updates any more unfortunately.

Anyway, if you read up on the knowledge base I linked you to, that will explain the HTTPS issue with the older cards. If IE8 works fine for ISX manager beyond that, then keep using that and figure out the best way for you to address the HTTPS issue. Let me know if you have any questions. After reading the article, let me know what you think. If you have many cards, I might have an option I can provide to you to automate the 1024 bit cert creation (which after you read FA162031 should make sense).

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:16 PM

0 Likes
0
1329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:16 PM

Thanks for the reply Angela.

That knowledge base article makes sense. I bet that's the issue because it just quit working out of the blue. I suppose right after the Windows update was rolled out to our machines.

We have about 100 cards(campus network), so an automated solution would be much appreciated. smile

Otherwise, what is the current APC replacement for the InfraStruxure Manager? We might be able to swing for the new hardware.

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:16 PM

0 Likes
0
1329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:16 PM

You'd want to look at StruxureWare Data Center Expert -> http://www.apc.com/products/family/index.cfm?id=350

They used to have a program where you could port over your nodes from ISX Manager to StruxureWare Central (now called Data Center Expert) but I am not sure if they still do that.

Anyway, if it's OK, I will contact you via email with our automated solution options.

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:16 PM

0 Likes
0
1329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:16 PM

Thanks for that info Angela. I will look into the Data Center Expert.

Also, I received your email.

You've been a huge help.

Thanks!

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:15 PM

0 Likes
0
1329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:15 PM

you're welcome!

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore