PowerChute network shutdown timing

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • PowerChute network shutdown timing
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5060
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
142
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:15 PM

0 Likes
2
1040
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:30 AM . Last Modified: ‎2024-03-05 11:15 PM

PowerChute network shutdown timing

Greetings,

I've set up a few test sites with the PowerChute network shutdown, but I'd like some clarification on some of the timing. None of the documentation I've read seems to exactly answer my question, hopefully you can help.

On my monitored UPS, I have set the Configuration -> Shutdown -> Low Battery Duration to 17 minutes. This bumps my Maximum Required Delay to 17 minutes.

On the vMA PowerChute Network Shutdown, I've set up the "Configure Shutdown" section with a value of 600 for the "The command file needs this much time to complete". I have not set up any events in "Configure Events" to cause the shutdown script to run, I'm relying on the PowerChute shutdown signal to come from the UPS.

Am I correct that as soon as the UPS reaches 17 minutes of run time it will send the PowerChute shutdown to all PowerChute clients?

This would give vMA 10 minutes to run the VM shutdown script, and then it would shut down the hosts after, is that correct?

Is there any reason to make the vMA PowerChute run the shutdown script if the UPS goes to battery since it's already going to receive a shutdown from the UPS once the "Low Battery Duration" threshold is reached?

Just want to make sure I have the timings correct and that I'm understanding the relationships between these values, thanks for the help.

Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • powerchute_network_shutdown
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:31 AM . Last Modified: ‎2024-03-05 11:15 PM

0 Likes
0
1040
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:31 AM . Last Modified: ‎2024-03-05 11:15 PM

You're understanding is correct. PCNS will tell the vMA to execute a RCLI event to shutdown your ESX box.

The low battery duration is when everything is forced to shutdown by the UPS if it hasn't been specifically configured to turn off earlier based on other actions.

Instead of running a script too, another VM shutdown instruction are in article FA159688 in our knowledge base @ http://www.apc.com/site/support/index.cfm/faq/ . Not sure if one is quicker than the other though.

This general timeline might also help too. It is in your PCNS help file.

1100_timeline1.jpg

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:31 AM . Last Modified: ‎2024-03-05 11:15 PM

0 Likes
0
1041
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:31 AM . Last Modified: ‎2024-03-05 11:15 PM

You're understanding is correct. PCNS will tell the vMA to execute a RCLI event to shutdown your ESX box.

The low battery duration is when everything is forced to shutdown by the UPS if it hasn't been specifically configured to turn off earlier based on other actions.

Instead of running a script too, another VM shutdown instruction are in article FA159688 in our knowledge base @ http://www.apc.com/site/support/index.cfm/faq/ . Not sure if one is quicker than the other though.

This general timeline might also help too. It is in your PCNS help file.

1100_timeline1.jpg

Reply

Link copied. Please paste this link to share this article on your social media post.

BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-07-01 02:31 AM . Last Modified: ‎2024-03-05 11:15 PM

0 Likes
0
1040
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 02:31 AM . Last Modified: ‎2024-03-05 11:15 PM

Thank you for the clarification.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore