APC Smart-UPS 5000VA RM Noise on battery

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • APC Smart-UPS 5000VA RM Noise on battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-30 11:59 PM . Last Modified: ‎2024-03-06 03:06 AM

0 Likes
4
2608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:59 PM . Last Modified: ‎2024-03-06 03:06 AM

APC Smart-UPS 5000VA RM Noise on battery

Hi!

I wonder if it is normal for the UPS to produce a buzzing noise when it's running on batteries?

The batteries in the unit are in bad condition and I wanted to make sure that the UPS is okay before swapping the batteries. 

I recorded an video of the sound, its easier to diagnostic the sound that way.

Labels
  • Labels:
  • Smart-UPS & Symmetra LX | RM
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2021-07-01 12:00 AM . Last Modified: ‎2024-03-06 03:05 AM

0 Likes
0
2607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:00 AM . Last Modified: ‎2024-03-06 03:05 AM

I thank you all for the informative responses. 

So the sound isn't normal. I will try to figure out what the cause of the noise is, hopefully I can fix it. I don't believe that something is wrong with the fan/fans, they/it don't seem to make any buzzing sound.

The ups works fine, except for the batteries, Im just worried that it will break or break any of the server that the unit is hooked up to. 

I will try to get it out of the rack and record the sound in a silent environment, but I doubt it will help diagnos the unit and find out what's wrong with it, or if something is just lose.  

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
BillP
Administrator BillP Administrator
Administrator

Posted: ‎2021-06-30 11:59 PM . Last Modified: ‎2024-03-06 03:06 AM

0 Likes
0
2607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-30 11:59 PM . Last Modified: ‎2024-03-06 03:06 AM

Hi Robert,

Thanks for taking the time to do the video. It was hard for me to tell specifically what the buzzing sounded like because of the other general noise though. I did not hear anything very alarming but it does sound slightly different than my UPS of this type. It is normal for it to sound different when the inverter kicks on. The other thing you could do is make sure the noise is not because of a dirty fan and maybe clean it with compressed air for good measure.

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-07-01 12:00 AM . Last Modified: ‎2024-03-06 03:05 AM

0 Likes
0
2607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:00 AM . Last Modified: ‎2024-03-06 03:05 AM

I've encountered some variation in the way the inverter transformers in the UPS are "potted" (for others: filled with varnish, epoxy, etc.) which causes the laminations to buzz when the UPS goes to battery. As long as the buzz is constant (volume, pitch, etc.) it is probably fine, as you say.

The main reason I posted this reply is because of the "clean the fan" suggestion. I see a fair amount of equipment that comes in here with problems due to inexperienced people cleaning the fans, so I wanted to provide some advice:

  • Do the cleaning with the device powered off (and fan not turning) and prevent the blades from spinning when blowing the dust off. If you have a spare "straw" from another air can, you can use this to hold the blades still while spraying with the duster. Overspeed can damage these fans in a number of different ways, mostly due to bearing failure but sometimes by damaging the speed sensor.
  • Wait for the unit to cool down completely - the gas that comes out of dusters is very cold and you can damage / destroy components from "thermal shock" if they are at an elevated temperature and then get a blast of cold gas. Likewise, wait for the part(s) you sprayed to come back to room temperature before powering it back on. You can probably feel the temperature of the air can to decide when it is safe to power the unit back on. Remember, the fan is designed to move air past heat-sensitive components, so when you spray "the fan", the gas will also move past those same heat-sensitive components.
  • Unless the fan has "spanish moss" hanging off it, cleaning it will normally only be a cosmetic function. The most common problem with fan speed comes from bearing issues, either grit has gotten into the bearing or the bearing simply wore out. In those cases, the fan needs to be replaced.
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 12:00 AM . Last Modified: ‎2024-03-06 03:05 AM

0 Likes
0
2607
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:00 AM . Last Modified: ‎2024-03-06 03:05 AM

that sound can be produced by many things in UPS....but generally its caused by coils and transformers......but it can be a filtering MKP capacitor...

if you dont have a "spot-microphone"  then there is a simple way how to find the noising spot.....get some rubber or plastic but flexible pipe....like 50-60cm is enough....put one side in your ear, and with other side go around from component to component till you hear in your ear the one that produces the loudest noise of that.... (a primitive stetoscope)

if it is a coil...then you should see is there a way to tight it, maybe even some cold solder can be cause....so check that too....anyway, you can get a transparent "electric transformer lacquer" that is used for wires and transformers, and simply paint it, when it dries, it will tight the coil and stop making that noise....

where to find a mentioned lacquer?! ...in any repair shop where they repair electro-motors and producing transformers etc....just ask the owner to give you a spoon of lacquer and it should be enough for your needs 🙂

Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-07-01 12:00 AM . Last Modified: ‎2024-03-06 03:05 AM

0 Likes
0
2608
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-07-01 12:00 AM . Last Modified: ‎2024-03-06 03:05 AM

I thank you all for the informative responses. 

So the sound isn't normal. I will try to figure out what the cause of the noise is, hopefully I can fix it. I don't believe that something is wrong with the fan/fans, they/it don't seem to make any buzzing sound.

The ups works fine, except for the batteries, Im just worried that it will break or break any of the server that the unit is hooked up to. 

I will try to get it out of the rack and record the sound in a silent environment, but I doubt it will help diagnos the unit and find out what's wrong with it, or if something is just lose.  

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore