Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey
NMC and servers not turning on after graceful shutdown
APC UPS Data Center & Enterprise Solutions Forum
Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-0112:03 AM. Last Modified: 2024-03-0603:05 AM
NMC and servers not turning on after graceful shutdown
Hi folks,
This hopefully isn't your standard PCNS server shutdown question!
I currently have many NMC cards within my environment managing many servers. I've been doing some tests today as although the shutdown of the servers when the power fails works really well and if the UPS turns off, all the servers come back; there is an issue when the power only goes off for a short amount of time (and here it is)......
1) My servers are set to turn off after five minutes on battery with a two minute delay (they turn off after seven minutes)
2) Power is restored in the ninth minute (example)
3) The Smart UPS waits approximately two to three minutes and then does it's restart action
4) The only server that powers on is a Dell PowerEdge 1850 that does NOT have a hot plug redundant power supply
All my other Dell servers - 1800, 1950, 2950 etc all have hot plug redundant power supplies and they do not register the UPS reboot and so do not power on!
All the BIOS settings are correct and the system works if the UPS turns off, but in my example above, it does not work!!
I have put the issue down to the UPS restart not being long enough (it only takes about a second) and I believe that the residual power in the redundant power supplies in the servers mean they do not register the UPS reset/power reset and hence do not power on.
Is there any way to configure the UPS reset to last 5 seconds, or 10 seconds, or even power itself off for a minute and then come on. This would resolve the issue.
I cannot see any other way of doing this but would appreciate any input. One other 'unclean' solution is to use the Power off UPS settings on the client, but I cannot guarantee all servers are shut down in time, so this really isn't an option!
Thanks for all your help
Rob
P.S I'm running the lastest firmware and PCNS software and this makes no difference