I'm looking at getting a Smart-UPS 5000VA to protect the kit in our rack... this is the 240v UK model and requires a hardwired connection with a maximum of 32A.
We currently have 2 16A commando type sockets in the server room and I was wondering as we arent going to be drawing more than 3100 Watts would a 16A connection be suitable for the UPS or do I need to get a 32A supply installed into the server room?
Any help would be appreciated!
Matt
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:24 AM . Last Modified: 2024-03-10 11:25 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:24 AM . Last Modified: 2024-03-10 11:25 PM
Another quick question regarding this unit, do i actually have to have it hardwred to the branch circuit or could i hardwire a commando plug lead to the UPS and then connect to this an existing 16A commando socket?
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:24 AM . Last Modified: 2024-03-10 11:25 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:24 AM . Last Modified: 2024-03-10 11:25 PM
Should be fine but take into account efficiency and approx 10% of UPS rating for the recharge draw after mains failure. Also realise if someone plugs test equipment etc you may trip it whereas you prob wouldn't with the 32a supply.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:24 AM . Last Modified: 2024-03-10 11:25 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:24 AM . Last Modified: 2024-03-10 11:25 PM
I thought that would be the case, i had already factored most of this in, typical draw is approx 2400W and I added 600W for battery replacement scenarios and rounded up to 3100W..... if my calculations are right a 16A commando should be good for 3680W @ 240V..... I just wanted someone else to verify that what I thought was right is indeed right! lol.... Cheers!
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:24 AM . Last Modified: 2024-03-10 11:25 PM
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-30 02:24 AM . Last Modified: 2024-03-10 11:25 PM
Another quick question regarding this unit, do i actually have to have it hardwred to the branch circuit or could i hardwire a commando plug lead to the UPS and then connect to this an existing 16A commando socket?