AP9631 Network Interface restarted

APC UPS Data Center & Enterprise Solutions Forum

Schneider, APC support forum to share knowledge about installation and configuration for Data Center and Business Power UPSs, Accessories, Software, Services.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • APC UPS, Critical Power, Cooling and Racks
  • APC UPS Data Center & Enterprise Solutions Forum
  • AP9631 Network Interface restarted
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
BillP
Administrator BillP Administrator
5059
voidstar_apc
Janeway voidstar_apc
196
Teken
Kirk Teken
146
View All

Recommended Forums

  • APC UPS for Home and Office Forum

  • EcoStruxure IT Forum

Free

English

Data Center Certified Associate Exam Development Path

Strengthen your foundational knowledge in Data Centers for free, enroll in this path today and start your learning journey!

4.0
Register Browse SE University

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to APC UPS Data Center & Enterprise Solutions Forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:50 PM

0 Likes
5
6036
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:50 PM

AP9631 Network Interface restarted

I have an AP9631 that seems to "Network Interface restarted" every couple days or so.  I have upgraded the firmware to v.6.4.6 , but this has not solved the issue. I looked through the logs files but dont see anything helps narrow down where the problem is. 

I am attaching the sanitized files if anyone could help narrow down the issue. 

Thanks

Attachments
Labels
  • Labels:
  • UPS Management Devices & PowerChute Software
  • Tags:
  • ap9631
  • resetting
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Philipp_apc
Ensign Philipp_apc
Ensign

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

0 Likes
0
6027
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

@APC I could reproduce the behavior again and got a core dump where should I send the snapshot?

Snippets:

dump.txt

09/07/2018 10:17:26 Failsafe Reset
Specific code = 200


AOS v6.5.6 rpdu2 v6.5.6
Serial Number: 5A1750E04651
AOS Binary Date/Time: Mar 30 2018 16:51:08
APP Binary Date/Time: Apr 24 2018 11:42:41

Task Dump Task ID 166



 Data in RAM is incomplete - dump aborted!

events.txt:

09/12/2018    21:53:37    System    Network Interface restarted.    0x0002 (occurs multiple times)

debug.txt:

09/12/2018 21:20:27 Requested Reset 
09/12/2018 21:53:38 Failsafe Reset
09/12/2018 22:49:52 Failsafe Reset
...
09/07/2018 09:18:33 .\os\os_heap.c:191 check_heap: block size mismatch. 09/07/2018 09:18:40 Software Exception Reset
09/07/2018 10:14:21 
Less than 100 bytes in stack, task 220

See Answer In Context

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
Anonymous user
Not applicable

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:50 PM

0 Likes
0
6029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:50 PM

There's a watchdog timer built into the AP9631 platform. If the network is quiet enough, it might sense the lack of traffic as a problem and restart the management card. There is also a ping test that takes place from time to time and a failure there could also restart the card.

Reply

Link copied. Please paste this link to share this article on your social media post.

voidstar_apc
Janeway voidstar_apc
Janeway

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

0 Likes
0
6029
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

It looks like a known issue with that firmware -- you could try reducing notifications ie removing SNMP trap receivers and email recipients.

Reply

Link copied. Please paste this link to share this article on your social media post.

Philipp_apc
Ensign Philipp_apc
Ensign

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

0 Likes
0
6030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

Will there be a possibility to disable this watchdog and/or ping feature in the future?

I tried to disable all unecessary services: ftp, snmp but I still get the network card restart and it takes up to 4 minutes

It is especially annoying for me because I use the APC7920B in automated tests which then fail because I cannot connect to the device when the interface is restarting.

Additional information:

aos: v6.5.6

rpdu2g: v6.5.6

bootmon: v1.0.8

Reply

Link copied. Please paste this link to share this article on your social media post.

Terry_Kennedy_apc
Commander Terry_Kennedy_apc
Commander

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

0 Likes
0
6030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

If you request a "Technical Support Debug Information Download" from the About / Support web page on your device, you'll get a .tar.gz file which contains a number of useful things. I don't remember which file it is (maybe the debug one), but one of them has a code identifying the cause of the watchdog reset. One of the APC folks can probably look that up for you and tell you why your card is resetting.

Reply

Link copied. Please paste this link to share this article on your social media post.

Philipp_apc
Ensign Philipp_apc
Ensign

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

0 Likes
0
6028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-29 06:15 AM . Last Modified: ‎2024-03-12 11:49 PM

@APC I could reproduce the behavior again and got a core dump where should I send the snapshot?

Snippets:

dump.txt

09/07/2018 10:17:26 Failsafe Reset
Specific code = 200


AOS v6.5.6 rpdu2 v6.5.6
Serial Number: 5A1750E04651
AOS Binary Date/Time: Mar 30 2018 16:51:08
APP Binary Date/Time: Apr 24 2018 11:42:41

Task Dump Task ID 166



 Data in RAM is incomplete - dump aborted!

events.txt:

09/12/2018    21:53:37    System    Network Interface restarted.    0x0002 (occurs multiple times)

debug.txt:

09/12/2018 21:20:27 Requested Reset 
09/12/2018 21:53:38 Failsafe Reset
09/12/2018 22:49:52 Failsafe Reset
...
09/07/2018 09:18:33 .\os\os_heap.c:191 check_heap: block size mismatch. 09/07/2018 09:18:40 Software Exception Reset
09/07/2018 10:14:21 
Less than 100 bytes in stack, task 220
Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore